APC, Stulz, Data Aire... All are inferior to Liebert in my opinion.
Also, in-row cooling designs are the way to go.
LIEBERT IS THE CADILLAC OF CRITICAL ROOM COOLING!
-
01-06-2013, 01:59 PM #15
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
410a systems are even more prone to clogging LL driers.
-
01-06-2013, 02:04 PM #16
Regular Guest
- Join Date
- Mar 2012
- Location
- Georgia
- Posts
- 20
May have got away with it using 22, but never with 410 & POE oil. We fix a lot of these after poor install. Purge with nitro during all pipe work. Triple evac & use ACCURATE micron gauge.
ONLY 2 things are meant to be in a working refrigeration system.....refrigerant & oil!