11-18-2012, 07:02 PM #1
how to warm up a centrifugal
I need to do an oil change on a CVHE. There is no hot water available near the chillers, so I need to find a portable water heater solution to warm the barrel. Preferably without taking 6 hours. Anyone have a piece of equipment they recommend? I think a propane heater would work the best, as the only power sources nearby are 120v or feeds equipment. Thanks.
-
11-18-2012, 08:14 PM #2
http://www.westsidewholesale.com/plu...osch-rp7p.html
You could mabey use some thing like this just a thought.Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
11-18-2012, 08:21 PM #3
You don't need to pressurize a low pressure chiller to do an oil change. You can do it in about 30 minutes with the machine in a vacuum if you've got the right tools.
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
11-18-2012, 08:59 PM #4
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 866
-
11-19-2012, 04:50 AM #5
The real simple way is to start the machine get it down to 45 deg. chw nice vacumm shut it down and work on it. You need to be quick about it.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
11-19-2012, 06:47 AM #6
Professional Member*
- Join Date
- Feb 2006
- Location
- Float'N Vally, MS
- Posts
- 1,601
-
11-19-2012, 11:49 AM #7
One of the guys who used to come on this board had a 123 refrigerant drum that he converted to a vacuum chamber with isolation valves on the inlet and outlet. He would evacuate the drum to a pressure lower than the chiller, open the isolation valve, and it would suck the oil right out of the chiller. Use the vacuum in the chiller to draw the new oil in.
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
11-19-2012, 04:25 PM #8
Invest in a good gear pump and your troubles will be over.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
11-19-2012, 04:29 PM #9
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,104
-
11-19-2012, 05:03 PM #10
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 866
We also use an oil transfer pump.
-
11-19-2012, 07:26 PM #11
bluke1 - Okay here it is, no hot water generation needed only 120 volt outlet. From the sump valve on the oil tank connect a 1/2" refrigerant hose to a gear pump inlet side with a check valve on the discharge side to prevent back flow. Leave the sump valve closed at this point. Install a line from the check valve outlet with a sight glass on the end and connect to a vacuum pump, if you have any ball valves that would help. Start the vacuum pump and once the vacuum drops below the level of the sump pressure open the sump valve and watch for oil moving to the sight glass. Valve off the sight glass, shut off the vacuum pump and start the gear pump and drain your 7 gallons into a 100 # refrigerant can (now a waste oil drum) . This doesn't take long, but once your pump looses prime your done. Your can either suck the new oil in or valve off the sump and reverse the gear pump and pump the oil back in the sump. Just remember to purge the air out of the connection at the oil sump before opening that valve. I always pump the oil in as I know I won't get air in the sump. Good luck- GEO
Of all the things I have lost in my life, I miss my mind the most-GEO
-
11-20-2012, 08:51 AM #12
Thanks for the advice. I have researched the question before I asked here. The local trane office told me that their method was to warm the chiller. I have searched gear pumps, but most seemed too large, high gpm. Can anyone be specific on the manuf. and model of the pump you are using?
-
11-20-2012, 09:26 AM #13
bluke- You don't need a high dollar hydraulic oil pump, I have a 1/2 hp, 120volt pump that came from W.W,Grainger. Yes, it is preferable to heat the entire vessel up as then you can also do a leak check. bluke please remember though you ask for advice and got it. The guys on hvac-talk.com have years of experience doing this and have been in your situation long before we had this easy method of getting professional advice. I have almost 30 years myself and I still request information from others. Like the man said "Ain't none of us as smart as all of us". I am a professional technician in training and will be for years to come. Good luck -GEO
Of all the things I have lost in my life, I miss my mind the most-GEO