Thread: 13 SEER vs. 16 SEER

  1. #21
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    Quote Originally Posted by esabet View Post
    Heating with hot water coil brings in humidification and, therefore, a more comfortable heat while a standard furnace is "dry" heat and not very comfortable.
    arrgh! I see this recommendation SOOO often, and it's TOTALLY FALSE! a hot water heating system is exactly the same humidity to the house as any other type of heating system.
    I hear many stating that the lower temp of the water radiators don't vaporize the water in the house like a high temp furnace heat exchanger or electric strip will... false.
    household humidity is determined by the amount of water in the home, and the temp of the air. you warm the air without adding humidity, and you get a lower relative humidity in the house. period.
    tight leak free houses have higher humidity in the winter because the cooking/bathing/breathing we humans do, gets better retained than the houses that leak outside air in all the time.

    water is a better conductor of heat, so it's more efficient at transferring heat from the fuel used to the air. that is the reason so many northern climate areas use it.
    STEAM radiators do tend to release humidity when they vent, but if you check out most homes with steam radiators, you will find they have racks for water trays to add humidity to the house... it's not the heat source doing the humidifying, it's the rack of water evaporating...
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  2. #22
    Join Date
    Nov 2012
    Posts
    12
    Post Likes
    Thread Starter
    Quote Originally Posted by vstech View Post
    arrgh! I see this recommendation SOOO often, and it's TOTALLY FALSE! a hot water heating system is exactly the same humidity to the house as any other type of heating system.
    I hear many stating that the lower temp of the water radiators don't vaporize the water in the house like a high temp furnace heat exchanger or electric strip will... false.
    household humidity is determined by the amount of water in the home, and the temp of the air. you warm the air without adding humidity, and you get a lower relative humidity in the house. period.
    tight leak free houses have higher humidity in the winter because the cooking/bathing/breathing we humans do, gets better retained than the houses that leak outside air in all the time.

    water is a better conductor of heat, so it's more efficient at transferring heat from the fuel used to the air. that is the reason so many northern climate areas use it.
    STEAM radiators do tend to release humidity when they vent, but if you check out most homes with steam radiators, you will find they have racks for water trays to add humidity to the house... it's not the heat source doing the humidifying, it's the rack of water evaporating...
    Wow, thank you for the detailed clarification. It makes much sense.

    All that said, what is your opinion on the SEER selection as I have it outlined?

  3. #23
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by esabet View Post
    ..., what is your opinion on the SEER selection as I have it outlined?
    What's the electric $$$/ kW?

    Higher SEER is not likely to make a noticable COMFORT difference on Long Island.
    What is your goal on IAQ, R.H. and temperature set-point?
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  4. #24
    Join Date
    Nov 2012
    Posts
    12
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    What's the electric $$$/ kW?

    Higher SEER is not likely to make a noticeable COMFORT difference on Long Island.
    What is your goal on IAQ, R.H. and temperature set-point?
    Here is the electric rate:

    Name:  Electric Rate.PNG
Views: 1994
Size:  5.8 KB

    I am going to sound dumb now but what are IAQ and R.H.? As for Temp set-point, we like to keep the house at about 72 degrees. The house has a southerly exposure with lots of windows.

    Hope that helps.

    P.S. We had a Manual J Report prepared, would that help?

  5. #25
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Rheem's M coils (Multiflex) are now gone. They were great coils. The N coils that are used now are very restrictive. Takes a strong blower to overcome the restriction to them.

  6. #26
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by esabet View Post
    Here is the electric rate:

    Name:  Electric Rate.PNG
Views: 1994
Size:  5.8 KB

    I am going to sound dumb now but what are IAQ and R.H.? As for Temp set-point, we like to keep the house at about 72 degrees. The house has a southerly exposure with lots of windows.

    Hope that helps.

    P.S. We had a Manual J Report prepared, would that help?
    IAQ = Indoor Air Quality
    R.H. = Relative Humidity

    http://www.lipower.org/pdfs/account/rates_resi.pdf

    LIPA - Long Island Power Authority
    I believe you need to use a heat pump and use LIPA ( provided that's ACTUALLY your utility) rate R883

    Rate 883/D883 - Residential, Water & Home Heating w/Heat pump
    Applies to customers who use electricity for both water and space heating with an electric heat pump,
    with the exception of fireplaces and coal/wood burning stoves,
    and account must have been established after January 26, 1983.

    Service Charge: Standard Rate ___$0.3600 $0.3600
    Service Charge: “D” rate ________$0.1790 $0.1790

    580/D580/581/D581 • 882/D882/883/D883

    Time Period ___________________ June 1 - Sept. 30 ______________ Oct. 1 - May 31
    Energy Charge: (per kWh)
    First 250 kWh _________________ $0.0857 ________________________ $0.0857
    Next 150 kWh _________________ $0.0975 ________________________ $0.0787
    Excess 400 kWh _______________ $0.0975 ________________________ $0.0515

    With a Manual J report, a realistic estimate of monthly cooling & heating $$$ can be provided based on using a SEER 13/ HSPF ~ 8.5
    and Heating & Cooling Degree Days.

    Or perhaps, the Manual J report may have the annual energy use embedded in it somewhere.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  7. #27
    Join Date
    Nov 2012
    Posts
    12
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    IAQ = Indoor Air Quality
    R.H. = Relative Humidity

    http://www.lipower.org/pdfs/account/rates_resi.pdf

    LIPA - Long Island Power Authority
    I believe you need to use a heat pump and use LIPA ( provided that's ACTUALLY your utility) rate R883

    Rate 883/D883 - Residential, Water & Home Heating w/Heat pump
    Applies to customers who use electricity for both water and space heating with an electric heat pump,
    with the exception of fireplaces and coal/wood burning stoves,
    and account must have been established after January 26, 1983.

    Service Charge: Standard Rate ___$0.3600 $0.3600
    Service Charge: “D” rate ________$0.1790 $0.1790

    580/D580/581/D581 • 882/D882/883/D883

    Time Period ___________________ June 1 - Sept. 30 ______________ Oct. 1 - May 31
    Energy Charge: (per kWh)
    First 250 kWh _________________ $0.0857 ________________________ $0.0857
    Next 150 kWh _________________ $0.0975 ________________________ $0.0787
    Excess 400 kWh _______________ $0.0975 ________________________ $0.0515

    With a Manual J report, a realistic estimate of monthly cooling & heating $$$ can be provided based on using a SEER 13/ HSPF ~ 8.5
    and Heating & Cooling Degree Days.

    Or perhaps, the Manual J report may have the annual energy use embedded in it somewhere.
    Wow, thanks.

    We never thought about H.R. or IAQ. How would a lay person establish the IAQ and H.R. anyway? We do intend to use ERV systems on both 1st and 2nd floor but that is because many are recommending it to us.

  8. #28
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    I.A.Q. is addressed by ASHRAE Standard 62.2

    CA version ..
    http://www.energy.ca.gov/2010publica...0-2010-006.PDF

    The process for exhaust-only ventilation system design is to: (1) determine the minimum
    amount of airflow required: (2) select a fan or multiple fans that are rated to provide ventilation
    airflow that equals or exceeds the minimum required; and (3) design and install a ventilation
    duct system that meets the requirements of ASHRAE 62.2 Table 7.1.

    (I.1) Whole-Building Ventilation Requirement Calculations
    Equation 4.1a
    from ASHRAE 62.2:

    Qfan = 0.01 x Afloor + 7.5x(Nbr + 1)
    Where: Afloor = conditioned floor area, ft²
    Nbr = number of bedrooms; not to be less than one

    Qfan = ventilation airflow requirement = minimum fan airflow rating, (CFM)

    Example 1
    2,500 sf house with 5 bedrooms
    Qfan = 0.01 x 2500 + 7.5 x (5 + 1) = 25 + 45 = 70 CFM

    Example 2
    2,000 sf house with 3 bedrooms
    Qfan = 0.01 x 2000 + 7.5 x (3 + 1) = 20 + 30 = 50 CFM
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •