Results 1 to 3 of 3
Thread: rheem and economisers
-
11-20-2012, 08:13 PM #1
Professional Member
- Join Date
- Jan 2008
- Location
- LEHIGH VALLEY, PA
- Posts
- 137
rheem and economisers
A Rheem 5 ton heat pump rtu , a couple of months old . An economiser was added to the unit , controlled via enthalpy on the damper inlet and a temp sensor. The site maintenace guy has found the econmiser opens up to 45 deg , even on very cold days , allowing a lot of cold air in to the office below. all settings as per rheem , checked another installed at the same time and the same thing is happening , ?, can you give me some advice please .
-
11-20-2012, 08:21 PM #2
what is the minimum pot set at......
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
11-20-2012, 09:29 PM #3
Professional Member
- Join Date
- Jan 2008
- Location
- LEHIGH VALLEY, PA
- Posts
- 137
Set at minimum position , i am new to rtu,s always worked on refrigeration and ductless systems , my understanding of the economiser , is that if the outdoor air conditions are good as checked by the enthalpy and temp sensor , when the system is in A/C, the damper will open and let outside air in for ;free cooling;, why is it operating in heating mode [heat pump] , thanks jim