Results 1 to 4 of 4

Thread: Engineered Air

  1. #1
    Join Date
    May 2009
    Location
    Waterloo Ontario
    Posts
    48

    Engineered Air

    hey guys, service call from today that has me stumped. The unit is an engineered air, model number to follow. The main burner is not lighting, so far this is as far as i have got.

    -Call for heat
    -Ventor starts
    -Pilot lights
    -Solenoid modulator opens
    -Gas Valve will not open, unit locks out on no flame.

    So, in the manual the gas valve is rated for 3-8vdc to open. (maxitrol). At the valve i am getting 34vdc, and the valve will not open! verified with manometer.
    The feed for this valve is straight off the main board. And yes, i am getting 34Vdc at the board as well.

    So is the board bad? or will adjusting one of the pots solve this issue? I have not heard back from tech support yet.

  2. #2
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    I am not familiar with this unit but it seems strange that the manual says 3-8vdc to open valve and you are reading 34vdc at the valve. My question is why are you getting 34vdc anywhere? It may have burned up the coil in the gas valve.
    Last edited by welling service; 11-19-2012 at 11:08 PM. Reason: add a thought

  3. #3
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,098
    Sounds to me like a failed power supply (regulator)...

    Probably to need a bit more information to be able to give better WAGS...

    GT
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  4. #4
    Join Date
    May 2009
    Location
    Waterloo Ontario
    Posts
    48
    unit model number is Engineered air DJ-60-0, serial number is M12815 Mua-2
    The board is a DJM 3.4.A, and the gas valve is a maxitrol M620