Page 2 of 2 FirstFirst 12
Results 14 to 15 of 15
  1. #14
    Join Date
    Jun 2012
    Post Likes
    Quote Originally Posted by Andy Schoen View Post
    Having been a TEV product mangler in my past life, yes I've seen this before. It is not common, however.

    With a heat pump system in the heating mode, and if a TEV is used to feed the indoor coil, discharge pressure will be transmitted to the underside of its diaphragm via the equalizer line.

    Normally this is not a problem for the valve.

    But if a recip compressor is being used, and if the recip compressor is delivering an inordinate amount of discharge pulsations... these pulsations work on the TEV powerhead. The powerheat casing flexes ever so slightly with these pulsations as if it were a drum. The weld succumbs...

    I don't ever recall this happening when a scroll compressor is used.
    Would a muffler help?

  2. #15
    Join Date
    Apr 2002
    Dallas, TX
    Post Likes
    Quote Originally Posted by Freightshaker View Post
    Would a muffler help?
    If the only tool you have is a hammer, you tend to see every problem as a nail. – Abraham Maslow

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Quality Home Comfort Awards