Results 1 to 13 of 15
Thread: Powerhead separation!!!!
-
11-20-2012, 06:58 PM #1
Powerhead separation!!!!
Ran across this valve today. It also dumped 6.5 lbs of r-22 into the ozone!!!Should i call the EPA?
-
11-20-2012, 07:05 PM #2
freakin' awesome! What unit was it in? Carrier?
-
11-20-2012, 07:16 PM #3
Wow, that's a first for me!!!
-
11-20-2012, 07:17 PM #4
Made in china?
-
11-20-2012, 07:25 PM #5
That's just the pressure relief valve doing its job.
-
11-20-2012, 07:26 PM #6
By chance was this valve on the indoor coil of a heat pump having a recip compressor?
The greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark. – Michelangelo
There are powers inside of you which, if you could discover and use, would make you everything you ever dreamed or imagined you could become. – Orison Swett Marden
Education is what remains after one has forgotten what one has learned in school. – Albert Einstein
-
11-20-2012, 07:41 PM #7
-
11-20-2012, 11:53 PM #8
Professional Member*
- Join Date
- Jan 2005
- Location
- southeast
- Posts
- 81
Never seen that before. I would think there has to be an abnormal amount of virbration to shake these parts apart. I don't believe the complete weld would break popping off the power assembly.
Just a thought take a good look of the system. There may be somthing going on !
-
11-21-2012, 12:11 AM #9
Very cool.
Sent from my SGH-T999 using Tapatalk 2
-
11-21-2012, 12:31 AM #10
-
11-21-2012, 05:55 AM #11
-
11-21-2012, 08:10 PM #12
Having been a TEV product mangler in my past life, yes I've seen this before. It is not common, however.
With a heat pump system in the heating mode, and if a TEV is used to feed the indoor coil, discharge pressure will be transmitted to the underside of its diaphragm via the equalizer line.
Normally this is not a problem for the valve.
But if a recip compressor is being used, and if the recip compressor is delivering an inordinate amount of discharge pulsations... these pulsations work on the TEV powerhead. The powerheat casing flexes ever so slightly with these pulsations as if it were a drum. The weld succumbs...
I don't ever recall this happening when a scroll compressor is used.The greater danger for most of us lies not in setting our aim too high and falling short; but in setting our aim too low, and achieving our mark. – Michelangelo
There are powers inside of you which, if you could discover and use, would make you everything you ever dreamed or imagined you could become. – Orison Swett Marden
Education is what remains after one has forgotten what one has learned in school. – Albert Einstein
-
11-22-2012, 10:17 PM #13
nice! thanks!
Spellin mitsakes bother me.


Reply With Quote