    Powerhead separation!!!!

    Ran across this valve today. It also dumped 6.5 lbs of r-22 into the ozone!!!Should i call the EPA?
    Attached Images Attached Images  

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,212
    freakin' awesome! What unit was it in? Carrier?

  3. #3
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Wow, that's a first for me!!!

  4. #4
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Made in china?

  5. #5
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,987
    By chance was this valve on the indoor coil of a heat pump having a recip compressor?
    If the only tool you have is a hammer, you tend to see every problem as a nail. Abraham Maslow

  6. #6
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,893
    Quote Originally Posted by Andy Schoen View Post
    By chance was this valve on the indoor coil of a heat pump having a recip compressor?
    It was on a Carrier energy recovery ventilator and yes it was the supply coil and it's a recip!!!

  7. #7
    Join Date
    Jan 2005
    Location
    southeast
    Posts
    83
    Never seen that before. I would think there has to be an abnormal amount of virbration to shake these parts apart. I don't believe the complete weld would break popping off the power assembly.
    Just a thought take a good look of the system. There may be somthing going on !

  8. #8
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,437
    Quote Originally Posted by Andy Schoen View Post
    By chance was this valve on the indoor coil of a heat pump having a recip compressor?
    Andy knows something that he is not sharing!
    How to make the perfect "Half-Hitch" knot or any other boyscout knot in 3 easy steps...

    1. Remove your meter leads from the meter and very carefully return them to their storage case or bag.
    2. Wait 2 seconds
    3. Very carefully remove your meter leads from their storage place and enjoy your new knot!

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,758

  10. #10
    Join Date
    Apr 2002
    Location
    Dallas, TX
    Posts
    2,987
    Quote Originally Posted by jayguy View Post
    Andy knows something that he is not sharing!
    Having been a TEV product mangler in my past life, yes I've seen this before. It is not common, however.

    With a heat pump system in the heating mode, and if a TEV is used to feed the indoor coil, discharge pressure will be transmitted to the underside of its diaphragm via the equalizer line.

    Normally this is not a problem for the valve.

    But if a recip compressor is being used, and if the recip compressor is delivering an inordinate amount of discharge pulsations... these pulsations work on the TEV powerhead. The powerheat casing flexes ever so slightly with these pulsations as if it were a drum. The weld succumbs...

    I don't ever recall this happening when a scroll compressor is used.
    If the only tool you have is a hammer, you tend to see every problem as a nail. Abraham Maslow

  11. #11
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,437
    nice! thanks!
    How to make the perfect "Half-Hitch" knot or any other boyscout knot in 3 easy steps...

    1. Remove your meter leads from the meter and very carefully return them to their storage case or bag.
    2. Wait 2 seconds
    3. Very carefully remove your meter leads from their storage place and enjoy your new knot!

  12. #12
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,365
    That's just the pressure relief valve doing its job.

  13. #13
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Very cool.


    Sent from my SGH-T999 using Tapatalk 2

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event