In response to an earlier question, my indoor dew point has been between 35F and 38F every time I've checked it for the last 3 days or so. It doesn't seem to change much.
-
12-24-2012, 11:53 AM #68
Regular Guest
- Join Date
- Jun 2009
- Location
- Albuquerque NM
- Posts
- 2,449
We had a party last week with ~30 people in the house. CO2 shot up to 2500 really fast and tripped the alarm. I couldn't find the instructions to set the alarm level up, so I just shut it off, but it would have been fun to see how high it would get.
-
12-27-2012, 12:55 PM #69
Regular Guest
- Join Date
- Jun 2009
- Location
- Albuquerque NM
- Posts
- 2,449
Here's a nice explanation of how CO2 sensor Automatic Background Calibration works, from Telaire:
http://www.telaire.com/refernce/appnotes/abclogic.htm
-
12-27-2012, 01:07 PM #70
Regular Guest
- Join Date
- Jun 2009
- Location
- Albuquerque NM
- Posts
- 2,449
And another one from AirTest:
https://www.airtest.com/support/refe...tocalpaper.pdf
-
12-29-2012, 10:51 AM #71
Good info. Also You can adjust the setting to low or higher enough to get activation with one person occupancy and calm winds.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
12-29-2012, 11:20 AM #72
Or you could open a window on an upper floor...hehehehee
-
12-29-2012, 12:17 PM #73
-
12-29-2012, 12:24 PM #74
Now your thinkin like a fitter! hehehe=eeee
-
04-25-2013, 12:33 PM #75
Regular Guest
- Join Date
- Jun 2009
- Location
- Albuquerque NM
- Posts
- 2,449
OK, I've been watching the CO2 levels for a while, and I see a lot of variation. So, I think using DCV (demand controlled ventilation) with the CO2 sensor would be good.
So, here's what I'd like to have:
- DCV ventilation to keep the CO2 at some level (800 PPM for example). This should allow in only enough outside air to keep the CO2 below the setpoint.
- Ventilation limits for low/high outside temperature and high outside dew point.
- An override with a higher ventilation rate. This would probably require a controlled fan on the duct (or an HRV/ERV).
My Prestige IAQ has nice features for limiting ventilation on low/high temperature and dew point, but that's it.
Maybe I need a HRV/ERV with the capability to take a CO2 sensor as input?
-
04-25-2013, 01:35 PM #76
-
04-25-2013, 02:33 PM #77
Regular Guest
- Join Date
- Jun 2009
- Location
- Albuquerque NM
- Posts
- 2,449
I think you could do something simpler, especially if a HRV/ERV is not needed. Let's say, for example:
A simple fresh air intake (filtered) for maintaining air quality based on CO2 levels. The intake flow could controlled by variable damper driven by the output from a 2-10V CO2-sensor. It could also be limited by the temperature/dewpoint limits of the Prestige IAQ if desired. This would be automatic and run continuously. The slight positive pressure shouldn't be a problem and might even be desirable.
Since that would only supply enough fresh air for maintaining IAQ under normal conditions, maybe you could add an additional fresh air intake with a duct fan that could be switched on when needed (for parties, cooking, etc.). This would create significant positive pressure so you would probably need to open a window when you run it, or put in a barometric output damper if you want it to be "automatic".
-