    samsung ac split m/n aqv18nsdxkcv trips on low refrigerant in cooling mode with the lowside pulling into a vacum, yes you would think its low on gas but on off cycle equalizing to 150lbs. i really wish there was a high side port but there is not. looks to me like there is no pumpdown solenoid aand the only restrictions could be in the 4way valve (yeah its a heatpump) or the exspansion valve. i hate a/c splits never worked on a samsung anyone out there have aany words of wisdom, it would be much appreciated

  2. #2
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,882
    Post Likes
    Just because it equalizes to 150 lbs in off cycle doesn't mean it's not low on gas. Checking the subcooling will determine if its low on gas or a restriction.

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,854
    Post Likes
    Moved to Tech to Tech.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,539
    Post Likes
    Pull the gas out. See if it's close to nameplate.
    Local 449?

  5. #5
    Join Date
    May 2003
    Location
    Charleston SC
    Posts
    143
    Post Likes
    Sounds like a classic restriction to me. You are no doubt aware the metering device is in the ODU. When you pull the refrigerant out, you can put your pressure taps any where you want them.
    Good luck
    Coolairman

  6. #6
    Join Date
    May 2010
    Location
    Oxford, UK
    Posts
    344
    Post Likes
    Quote Originally Posted by targetman View Post
    Pull the gas out. See if it's close to nameplate.
    Agreed, also there may well be another gauge port inside the unit, take the cover off and see. Make sure all the plugs are inplace on the circuit boards and the head is on the EEV (assuming its an inveeter unit). Does it work ok in heating mode?

    Used to see a few problems with blocked strainers just before the capilary tube on older R22 splits (various makes) but not really had the problem with the R410A stuff.

  7. #7
    Join Date
    Jul 2012
    Location
    Chicago, IL
    Posts
    52
    Post Likes
    I ran into this same exact issue with a mitsubishi mini split and we found out it was a stuck exv and had to replace the coil in the head.