    vent draft regulator for oil furnace

    I haven't done a lot with oil furnaces so I ask lots of questions when I can. Is a draft regulator required for a vent pipe venting out the chimney?

  2. #2
    Join Date
    Jan 2006
    Location
    Powell River, BC, Canada
    Posts
    762
    Yes.
    Where are you? Are you done yet? I got ONE more call for you.....

  3. #3
    Join Date
    Jan 2011
    Location
    Boston, MA
    Posts
    459
    Yes, you need it in order to set your draft.

  4. #4
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    6,051
    Required by code unless specifically prohibited by the mfr. Must be set to a specific draft guided by a manometer. See Field Controls for more info.

  5. #5
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,384
    Should have one on everything. Also install a spill switch wired in series with the burner. Allow unit to run and get a hot flue. Then adjust draft to manufacturer specs. Check draft under the barometric or closest to the burner because this is the draft the barometric is controlling. most oil furnaces are set to -.02" w.c.

  6. #6
    Thank you everyone who responded to my thread. Sure is good to get quality answers on some unfamiliar topics.