    I haven't done a lot with oil furnaces so I ask lots of questions when I can. Is a draft regulator required for a vent pipe venting out the chimney?
    Jan 2006
    Powell River, BC, Canada
    Yes.
    Where are you? Are you done yet? I got ONE more call for you.....
    Jan 2011
    Boston, MA
    Yes, you need it in order to set your draft.
    S.E. Pa
    Required by code unless specifically prohibited by the mfr. Must be set to a specific draft guided by a manometer. See Field Controls for more info.
    Jul 2009
    Columbia, MD
    Should have one on everything. Also install a spill switch wired in series with the burner. Allow unit to run and get a hot flue. Then adjust draft to manufacturer specs. Check draft under the barometric or closest to the burner because this is the draft the barometric is controlling. most oil furnaces are set to -.02" w.c.
    Oct 2012
    Thank you everyone who responded to my thread. Sure is good to get quality answers on some unfamiliar topics.