Thread: York YS Power fault

  1. #1
    Join Date
    Nov 2012
    Posts
    3
    Post Likes

    Confused York YS Power fault

    Hello: York YS chiller keeps giving me a POWER FAULT on display. Chiller starts runs for 2-3 minutes then i get this power fault code? Chiller has a ssms model 5557l-46a. I have checked wiring between boards and found no problem that i could see. HELP!!!!!!!

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    this problem is usually related to the current transformers. watch your amp draw on the panel to see what it is doing during the start up and up to the 2-3 minutes before the fault occurs.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. #3
    Join Date
    Nov 2012
    Posts
    3
    Post Likes
    Thread Starter
    t1 548 t2-551 t3-551 amps at start before shut down t1-134 t2-114 t3-134 amps

  4. #4
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    From the operation manual:

    “LCSSS - POWER FAULT”The Liquid Cooled Solid State Starter Logic/Trigger
    Board has detected that the compressor motor current in
    one or more phases has decreased to <10% of the FLA
    for a minimum of 1 line cycle. This check is inhibited
    during the first 4 seconds of SYSTEM RUN and until
    the motor current is >25% of the FLA. The chiller will
    automatically restart upon completion of SYSTEM
    COASTDOWN.

    Like, jayguy said, check CTs and associated wiring from CTs to trigger board and BTW tou have a SSS7L-46A (not 555)

  5. #5
    Join Date
    Nov 2012
    Posts
    3
    Post Likes
    Thread Starter
    How do i check The CTs ?

  6. #6
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by SPD View Post
    How do i check The CTs ?
    got an ohm meter? look for loose connections. like KY posted, 1 line cycle is very quick and the panel will not update fast enough for you to see it. if everything seems ok, you may need to call in a heavy hitter.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •