Results 1 to 6 of 6
Thread: York YS Power fault
-
11-19-2012, 09:50 PM #1
New Guest
- Join Date
- Nov 2012
- Posts
- 3
York YS Power fault
Hello: York YS chiller keeps giving me a POWER FAULT on display. Chiller starts runs for 2-3 minutes then i get this power fault code? Chiller has a ssms model 5557l-46a. I have checked wiring between boards and found no problem that i could see. HELP!!!!!!!
-
11-19-2012, 11:23 PM #2
this problem is usually related to the current transformers. watch your amp draw on the panel to see what it is doing during the start up and up to the 2-3 minutes before the fault occurs.
The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
11-20-2012, 04:37 PM #3
New Guest
- Join Date
- Nov 2012
- Posts
- 3
t1 548 t2-551 t3-551 amps at start before shut down t1-134 t2-114 t3-134 amps
-
11-20-2012, 06:38 PM #4
Professional Member
- Join Date
- Jan 2011
- Posts
- 645
From the operation manual:
“LCSSS - POWER FAULT”The Liquid Cooled Solid State Starter Logic/Trigger
Board has detected that the compressor motor current in
one or more phases has decreased to <10% of the FLA
for a minimum of 1 line cycle. This check is inhibited
during the first 4 seconds of SYSTEM RUN and until
the motor current is >25% of the FLA. The chiller will
automatically restart upon completion of SYSTEM
COASTDOWN.
Like, jayguy said, check CTs and associated wiring from CTs to trigger board and BTW tou have a SSS7L-46A (not 555)
-
11-20-2012, 07:22 PM #5
New Guest
- Join Date
- Nov 2012
- Posts
- 3
How do i check The CTs ?
-
11-21-2012, 12:56 AM #6The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?


Reply With Quote