Results 14 to 17 of 17
Thread: Mcquay Cond press high alarm
-
11-20-2012, 01:50 PM #14
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
You may want to get someone experienced to look at this chiller. Your "corrected" pressure indicates reverse flow. Perhaps language is an issue here. I only speak English. I'm sorry, but my faith in our ability to properly communicate on the internet and to accurately discuss your problem is weakened. Maybe others here will be better able to help. The chances of that will be greatly increased if you translate from metric. Good luck.
-
11-20-2012, 04:34 PM #15
Regular Guest
- Join Date
- Nov 2012
- Location
- Albania
- Posts
- 11
i have upload a video of heat pump, 3 min after when increase stage up condenser press goes 18 bar and it stops for high press alarm. The link of video is :
-
11-27-2012, 03:56 AM #16
Regular Guest
- Join Date
- Nov 2012
- Location
- Albania
- Posts
- 11
Fixed , it was not proper water flow and not to much request for heating in this period.
-
11-27-2012, 09:00 AM #17
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
Glad to hear you got it fixed, and thanks for the update.


Reply With Quote