Results 14 to 26 of 27
    Nov 2011
    Moreno Valley Ca.
    like I said will find information and post when I get back to work. I was also surprised to see. Thanks for replies
    Nov 2011
    Moreno Valley Ca.
    oh ok
    Nov 2011
    Moreno Valley Ca.
    Funny but they keep dirt in this cooler for research purposes. Yes unit has reciever, rooftop condnser, yes it is a pump down system.
    Mar 2009
    Mid-Mo
    Does it have a headmaster for head pressure control?
    Nov 2011
    Moreno Valley Ca.
    No head pressure control. This really isnt one of the most difficult pieces of equipment at all. I just wanted to make sure i was doing everything correct before I go back and charge. Its only about 2 years old if that, and im already replacing a comp. Not sure what tech. did before me. Old comp. LRA amped. Could have been coincidence but i doubt it. Im pretty sure it was a charging issue the first time.
    Quote Originally Posted by Ken11 View Post
    Print out the document that I linked to earlier in this thread.
    Read it and follow the instructions.
    You will KNOW that the unit is charged properly.
    If you want to get into WHY the compressor has failed in such a short time, you'll need to give us a full set of system operating conditions once you've got it back online
    A lot of times, that headmaster valve is stuck back in the back and isn't easy to see on a first inspection.
    I don't know California's weather, but if your ambient drops much below 50F or so, you'll definitely need some sort of low ambient control to maintain a minimum liquid pressure.
    May 2009
    San Diego
    Copeland cares about compressor cooling. and recommends 30 dg sh, @ the comp. 1dg sh would be fine for protection.
    May 2009
    San Diego
    ABSORBTION........too funny.
    May 2009
    San Diego
    I think they call 404a a "near azeotrope" and so its fine.....However not the case for 414b.
    May 2011
    s.e. pennsylvania
    We protect it by keeping it cool and ensuring that no liquid returns, I'm just saying with a reefer system charging it by checking compressor sh is a poor practice. I'm not saying it shouldn't be checked but sh should be checked and set at the evap. If its set 10* at evap but running 45* at compressor then there needs to be secondary means of cooling the compressor.
    May 2009
    San Diego
    10-4, I agree. The original post was for some explanation on charging or rules of thumb. (not sure how to repost with my reply) So I gave a few. This not being a diy site, Didn't want to give to too much info. Just enough so anyone in the trade could find a few key points helpful. If we want to go crazy...I want pressures, sh, sc, amp draw, sight glass, were going see this box satisfy and make sure she pumps down. In the mean time if this isn't our account were checking the other equipment and working up a maintenance contract. Who was the last company out here?
    Nov 2012
    Tahlequah OK
    Copeland recommends a minimum 20 to 40 degrees compressor superheat. Within this range you should be able to get the right evap SH. Compressor SH always trumps evap SH. Is this 59 degrees the temp you want or the temp you are getting before topping the charge off?