    Working on a Copeland R404a 5x7 walk-in cooler maintaining 15C/59F. Have been getting mixed advice on charging techniques. I normally charge to subcooling specs and 20-40dg compressor SH. Am confused about the 10-20dg TD charging rule and how to use it. I understand all freezers have a 10dg TD and Medium to High temp use 15-20 TD Can someone please explaine? Thanks in advance

  2. #2
    Join Date
    May 2009
    Location
    San Diego
    Posts
    10
    Post Likes
    So many variables......I've really only seen the subcooling method applied to R410a, but thats another story. R404a......Charge with liquid to a full glass. No glass, 30dg over ambient. 10dg subcooling (optimal). As far as heat abortion "superheat"....freezer 7-9, cooler 10-12, a/c 12-15.
    Copeland says 30dg......sounds high to me, but they're the engineers.
    Hope that helps

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    5,858
    Post Likes
    Quote Originally Posted by crossthread View Post
    So many variables......I've really only seen the subcooling method applied to R410a, but thats another story. R404a......Charge with liquid to a full glass. No glass, 30dg over ambient. 10dg subcooling (optimal). As far as heat abortion "superheat"....freezer 7-9, cooler 10-12, a/c 12-15.
    Copeland says 30dg......sounds high to me, but they're the engineers.
    Hope that helps
    This should be in the ARP forum.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  4. #4
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Copeland recommends a minimum 20 to 40 degrees compressor superheat. Within this range you should be able to get the right evap SH. Compressor SH always trumps evap SH. Is this 59 degrees the temp you want or the temp you are getting before topping the charge off?

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    Tell me more about this unit...

    A 5x7 box maintaining 60 degrees? What purpose?

    Does it have a receiver? Is the condensing unit outdoors? Is it a pumpdown unit?


    Now, ASSUMING that it has a receiver, I'll make the following suggestion.

    Charge to a clear sightglass.

    Taking it further.

    IF the condensing unit is indoors, I'd add a small amount of refrigerant to handle temperature fluctuations.

    IF the condensing unit is outdoors, there's a whole nother bit of calculations that are required to properly charge the unit.

  6. #6
    Join Date
    Nov 2011
    Location
    Moreno Valley Ca.
    Posts
    10
    Post Likes
    Thread Starter
    Funny but they keep dirt in this cooler for research purposes. Yes unit has reciever, rooftop condnser, yes it is a pump down system.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    Quote Originally Posted by Ken11 View Post
    Funny but they keep dirt in this cooler for research purposes. Yes unit has reciever, rooftop condnser, yes it is a pump down system.
    Print out the document that I linked to earlier in this thread.

    Read it and follow the instructions.

    You will KNOW that the unit is charged properly.


    If you want to get into WHY the compressor has failed in such a short time, you'll need to give us a full set of system operating conditions once you've got it back online

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    27,197
    Post Likes
    Quote Originally Posted by Ken11 View Post
    Working on a Copeland R404a 5x7 walk-in cooler maintaining 15C/59F. Have been getting mixed advice on charging techniques. I normally charge to subcooling specs and 20-40dg compressor SH. Am confused about the 10-20dg TD charging rule and how to use it. I understand all freezers have a 10dg TD and Medium to High temp use 15-20 TD Can someone please explaine? Thanks in advance
    That is a great question, but I'd like to see you post it in the Pro forums. Get you post count up to 15 (only 12 posts to go) and we can answer that question.

    Hint: in refrigeration, the "TD" value uses the evaporator suction saturation temp, and in air conditioning, we use delta T, or the return air temp versus the supply air temp. It's a different approach to the subject.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  9. #9
    Join Date
    May 2011
    Location
    Spring City, Pennsylvania, United States
    Posts
    226
    Post Likes
    Crossthread- you are talking about sh taken at the evap, which is how it should be set on reefer system. Copeland cares about comp protection.

  10. #10
    Join Date
    May 2009
    Location
    San Diego
    Posts
    10
    Post Likes
    Copeland cares about compressor cooling. and recommends 30 dg sh, @ the comp. 1dg sh would be fine for protection.

  11. #11
    Join Date
    May 2011
    Location
    Spring City, Pennsylvania, United States
    Posts
    226
    Post Likes
    Quote Originally Posted by 2sac View Post
    This should be in the ARP forum.
    Man can't believe I missed that! Maybe in the aop roe v wade section

  12. #12
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Tell me more about this unit...

    A 5x7 box maintaining 60 degrees? What purpose?

    Does it have a receiver? Is the condensing unit outdoors? Is it a pumpdown unit?


    Now, ASSUMING that it has a receiver, I'll make the following suggestion.

    Charge to a clear sightglass.

    Taking it further.

    IF the condensing unit is indoors, I'd add a small amount of refrigerant to handle temperature fluctuations.

    IF the condensing unit is outdoors, there's a whole nother bit of calculations that are required to properly charge the unit.
    ^^
    Ya that....

  13. #13
    Join Date
    Nov 2011
    Location
    Moreno Valley Ca.
    Posts
    10
    Post Likes
    Thread Starter
    Ok will post in ARP forum, sorry. As for crossthrreads response to charge to a full sight glass, hmmm.... not too sure bout that. R-404a series refrigerants should never be charged to full sight glass based on research from this exact same problem. The first time I did just that and unit was overcharged. I believe i read that in Danfoss refrigeration basics or something. I will find and post. But i never really got an answer as to why you shouldnt charge this series to full glass. Is it due to blend, fractionization capabilities, pressure drop??