Page 6 of 6 FirstFirst 123456
Results 66 to 77 of 77
  1. #66
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    Quote Originally Posted by indy2000 View Post
    was the oil Gage fluttering?

    if there is refrigerant boiling out of the oil, you would see lower and possibly flutter in net oil pressure.
    No flutter in gage on oil pump port or CC pressure gage. No foaming in oil sight glass. Oil level remains fairly constant at 1/4 glass. Thanks for all of the suggestions. I still think it is a bearing problem. Two reasons I say this; 1. Oil pump pressure at comp start up=85 five mins or less into run=40 psi. Suction pressure=25psi and varies depending on how many LLSV's are calling. There are a total of 6 LLSV's on this system. 2. The sister comp which I just installed never drops in NPOP and they share a common hot gas and suction line. I replaced it because of bearing failure. The previous had jumps red the oil pressure controls. That was his way of solving problems. It just seems to me if there was an external reason for the comp. tripping on oil pressure it would be happening to both comp.

  2. #67
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    783
    Post Likes
    sounds like an oil return return problem, seeing you have lost a compressor already.

    you def want to get to the root problem, could be a piping issue.

  3. #68
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    783
    Post Likes
    r&r'ing a 40hp semi on monday, apparently the 4th in 3 years.

    Will be many hours of investigation before this one is left on its own, lack of lube.

    good luck with yours.

  4. #69
    Join Date
    Dec 2009
    Posts
    26
    Post Likes
    replace contactor! oil pressure is fine, one leg of contactor is bad, overload opens before the oil pressure switch, when you get there you manually reset oil, but the overload closed long time b4.

  5. #70
    Join Date
    Dec 2012
    Posts
    11
    Post Likes
    i sort of have the same problem with my TRANE 6 cyl. model E (open type) overhauling it right now i noticed a scratch on the oil line going to the seal end bearing but did not notice any problem with the bearings...could anyone help me on what to do with the scratch or should i just ignore it..i maybe off the topic sorry i am new to the forums

  6. #71
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,996
    Post Likes
    Quote Originally Posted by sweater View Post
    ... i noticed a scratch on the oil line going to the seal end bearing ...
    what do you mean by a 'scratch' on the oil line...on the copper line?
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  7. #72
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    What made the scratch? Is it deep enough to allow oil to escape? My copeland just quit tripping out on oil pressure and I don't know why. Once the weather cooled off a little it stopped tripping. I can't see any correlation between cooler weather and the problem with oil pressure. I never saw abnormal head pressure or suction pressure. It never ran hot so I can't see it going out on internal overload or high temp. The only abnormal thing I witnessed was a drop in actual oil pump pressure out put a few minutes after start up. Which leads me to suspect an internal oil leak.
    Last edited by welling service; 12-20-2012 at 11:44 PM. Reason: correction

  8. #73
    Join Date
    Dec 2012
    Posts
    11
    Post Likes
    Quote Originally Posted by jayguy View Post
    what do you mean by a 'scratch' on the oil line...on the copper line?
    yes sir that 1/4inch line that is coming from the oil pump it is not that deep though just need advice if i should go and weld it up thanks

  9. #74
    Join Date
    Dec 2012
    Posts
    11
    Post Likes
    i think it was from a previous failure though it has a scratch on the oil line no evidence from the bearings that i took out and replace that i lacked lubrication,,it is not deep enough for the oil to escape as per my inspection i need your opinion can i use metal epoxy to patch it up or just simply leave it as it is thank you sir for the reply

  10. #75
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,996
    Post Likes
    Since you do not have a picture, it is difficult to say. I would lean toward replace versus epoxy repair. If the scratch looks old and you aren't having any issues then it might be best to leave it alone.

  11. #76
    Join Date
    Dec 2012
    Posts
    11
    Post Likes
    Quote Originally Posted by jayguy View Post
    Since you do not have a picture, it is difficult to say. I would lean toward replace versus epoxy repair. If the scratch looks old and you aren't having any issues then it might be best to leave it alone.
    yup from the looks of it.. it is old since there were no large chunks of parts that broke that might have scratched it. anyways thank you very much and will post here whatever happens

  12. #77
    Join Date
    Dec 2012
    Posts
    11
    Post Likes
    well i started the compressor last night it went great i had 60psi back pressure an oil pressure of 140psi and a head of 250psi thanks for the advise my friends

Page 6 of 6 FirstFirst 123456

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.