Page 3 of 6 FirstFirst 123456 LastLast
Results 27 to 39 of 77
  1. #27
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,671
    Post Likes
    New oil pump. Did you use the right gasket?

    Have you checked for a pressurized crankcase?

    What does your contactor look like?

  2. #28
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,024
    Post Likes
    Quote Originally Posted by welling service View Post
    It starts up at about 85PSI and then drops to around 50 PSI. My CC pressure is about 25 PSI. I never see much variation in the suction pressure. It will run like this for various times and sooner or later trips on low oil pressure. It has run for two weeks one time before tripping. I have not had my gauges on it when it trips so I don't know if the pump output is going down or the CC pressure is coming up. I have done a piston blow by test and found no problem. The comp. pumps down just fine and holds. I thought maybe the OPC was bad so I installed a new one with the same results. The oil pump is newly installed because at first I thought the pump was worn and not maintaining pressure. I have never run up on this problem before and I don't mind saying I AM STUMPED!!
    it may not even be an oil related issue, maybe the compressor is tripping on overload, have you thought about that?

  3. #29
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Is this a part start motor?!

  4. #30
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,153
    Post Likes
    Quote Originally Posted by welling service View Post
    It starts up at about 85PSI and then drops to around 50 PSI. My CC pressure is about 25 PSI. I never see much variation in the suction pressure. It will run like this for various times and sooner or later trips on low oil pressure. It has run for two weeks one time before tripping...
    if it runs long enough that you can not catch it with your gages on it, then it is not a failed compressor. 25 psid is a fine pressure for the compressor...hell, 10 psid is fine as far as copeland is concerned. the question that i have is this: what was it 1, 2, 4 or more months ago and what is it now? it sounds to me like several issues may be happening here.

    how long does it take to drop from 60 psid to 25 psid? what is the application? are you watching the oil temperature while it runs? as the oil gets hotter, it thins out. that causes the net oil pressure to drop. you show up and the oil is 'cold' and all seems fine. perhaps your oil is also hanging up in the system some what.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  5. #31
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes


    Quote Originally Posted by jpsmith1cm View Post
    true knowledge exists in knowing that you know nothing.

  6. #32
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,671
    Post Likes
    Quote Originally Posted by supertek65 View Post

    You can't whistle cryptically.

    I'm already whistling cryptically, so quit copying me.

  7. #33
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    QUIT SAYING EVERYTHING 5 SECONDS BEFORE I SAY IT!!!!!!!!!!!!!!!!!!!!!!!!
    true knowledge exists in knowing that you know nothing.

  8. #34
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    No it is not a part winding start .

  9. #35
    Join Date
    Nov 2012
    Location
    Tahlequah OK
    Posts
    131
    Post Likes
    Thread Starter
    Yes I used the right gasket. I also did a piston blow by test and the CC pressure and suction pressure dropped at the same rate down to 0 psi. The oil temp is normal. The contactor is just fine. I reset the OPC last Friday and the unit has been running just fine. Checked NPOP today it was 15 PSI. Pump pressure 55PSI, CC pressure 40 PSI. Like I said the unit just takes a notion to run just fine for a while and then starts tripping the OPC. WE have had 29 degree nights and 50 degree nights for the past 3 days so I can't see ambient temp having anything to do with the tripping problem.

  10. #36
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,153
    Post Likes
    Quote Originally Posted by welling service View Post
    ...WE have had 29 degree nights and 50 degree nights for the past 3 days so I can't see ambient temp having anything to do with the tripping problem.
    low head pressure usually = low suction pressure. low suction pressure = low refrigerant flow rates. low refrigerant flow rates = poor oil return. poor oil return = no oil. no oil = 0 oil psid. < 10 psid = trip oil pressure switch. trip oil pressure switch = unhappy customer. unhappy customer = unhappy service tech.

    math is fun!
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  11. Likes GoCougs liked this post
  12. #37
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,395
    Post Likes
    Quote Originally Posted by jayguy View Post
    low head pressure usually = low suction pressure. low suction pressure = low refrigerant flow rates. low refrigerant flow rates = poor oil return. poor oil return = no oil. no oil = 0 oil psid. < 10 psid = trip oil pressure switch. trip oil pressure switch = unhappy customer. unhappy customer = unhappy service tech.

    math is fun!

    That's not math....That's Arithmaslick....
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  13. #38
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,671
    Post Likes

  14. #39
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by jayguy View Post
    low head pressure usually = low suction pressure. low suction pressure = low refrigerant flow rates. low refrigerant flow rates = poor oil return. poor oil return = no oil. no oil = 0 oil psid. &lt; 10 psid = trip oil pressure switch. trip oil pressure switch = unhappy customer. unhappy customer = unhappy service tech.

    math is fun!
    This is the only kind of math I actually understand!!!!!

Page 3 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.