Page 1 of 6 123456 LastLast
Results 1 to 13 of 77
    Nov 2012
    Tahlequah OK
    Question oil pressure problem
    I have a 10 ton Copeland discus and a 15 ton copelamatic on a rack system. This is a R22 system. They share a common hot gas line and suction line. The discus maintains a constant oil pressure out put at the pump of 90 pounds. The copelamatic on start up has a oil pressure output of about 85 pounds but it slowly falls and eventually trips my oil pressure control. The discus is a new compressor. The previous discus was doing the same thing. It busted one of the connector rods. The oil pump is new, I have a crank case heater on the comp and there is no foaming in the sight glass. The oil level is 1/2 way up the sight glass. I have installed a new oil separator on the system and it works great. This system is at a Save A Lot store and takes care of medium temp display boxes. It seems like there is an internal oil leak in the compressor causing the oil pressure to fall off. Has anyone encountered this problem before?
    broken connecting rod!!!!!!!!!!!!1
    sorry!
    but that is most likely your problem!
    frank
    NH
    Check the pressure difference between crankcase and suction valve... How new is this compressor?
    up in the hizzy
    I would drain the oil check the screen and the pump, it doesnt take long to do it!
    and you can reverse rotation too!!!!!!!!
    Quote Originally Posted by valdelocc View Post
    up in the hizzy
    Quote Originally Posted by supertek65 View Post
    Thats right, although there maybe gunk floating around.
    whats up with all the chillers avatars? I liked the pink donut better! chillers are the new hvac fashion!I'm a big boy working on big intimidating chillers blah blah blah if I ever get an avatar it would be a window shaker
    LMAO!!!!!!!!!! ROFL!!!!!!!!!!!!!
    i like this avatar because it is from a retrofit we did on a 47 year old chiller and the avatar is of the graphics on the adaptaview!
    really pretty cool! old retro graphics on an old retro chiller with modern controls!
    kind of abstract!
    Southeastern Pa
    Frank, that reminds me.
    I have to buy a bench grinder!!!!!!!
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jul 2009
    In a mechanical room....
    LOL
    “It takes courage to grow up and turn out to be who you really are.”
    - E.E. Cummings
    Quote Originally Posted by welling service View Post
    Couple things.
    #1. Telling us output pressure is, largely, meaningless. You need to properly measure NET oil pressure, or pump outlet pressure minus crankcase pressure. With a Copeland, that should be 50#.
    #2. This 'Copelametic' compressor... Well, a 15HP Copelametic doesn't tell me a whole lot. How about model numbers?
    While you're there getting the above information, do me a favor, IF the "copelametic" compressor is a 4D model (one with two heads) pump it down and pull the oil screen.
    I would think that, with a broken rod, you'd have a lot of noise and vibration which you haven't described.
    Nov 2012
    Tahlequah OK
    Looks like a Trane Centravac Chiller. When these old chillers are running just right with no air in the system they are the quietest chiller ever.
    kind of abstract!
    Nov 2012
    Tahlequah OK
    I know how to check net positive oil pressure. The pump out put pressure is the one that falls. The suction remains constant. Read the post a little closer. I said that the discus has been replaced because it was the one with the busted rod. I have pulled the oil screen and it is clean and I have changed the oil also. It is a 4D model with two heads.
    Couple things.