    Kerosene and flare fittings

    Did a call at a home today. The owner said there was fuel leaking from the fuel lines near the burner. Obviously that's dangerous so I was sent right over.

    Everything looked brand new. New fuel lines, new shutoff valves, new filter can etc.

    The furnace was in the basement, the old one had originally been inside the house. I found a few very slow leaks, very very slow. A drop would form maybe every 5 minutes or so on the bottom of the shutoffs and around the gasket on the filter. I took apart the offending flare joints and it looks like the guy who did the install did a good job. No splits, cuts, burrs or any of that. When I put the flares back together I put a little pro-dope on them since I couldn't think of anything better to do besides tighten them down as best as I could. I changed the filter and gaskets and that seemed to take care of the leak on the filter.

    Here are my questions:
    Is there anything about kerosene that would make it leak more than #2 fuel oil? It seems a little thinner than #2 and I thought it may leak in colder conditions. Kinda the way PEX piping can leak a little when it's cold. The basement was chilly, maybe in the 50s. Or could it sneak its way through the threads if there wasn't any thread dope?

    Was my thread dope idea ok? Some guys like the stuff and some guys don't. What's your take?

    Thanks

  2. #2
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by pavo6503 View Post
    Did a call at a home today. The owner said there was fuel leaking from the fuel lines near the burner. Obviously that's dangerous so I was sent right over.

    Everything looked brand new. New fuel lines, new shutoff valves, new filter can etc.

    The furnace was in the basement, the old one had originally been inside the house. I found a few very slow leaks, very very slow. A drop would form maybe every 5 minutes or so on the bottom of the shutoffs and around the gasket on the filter. I took apart the offending flare joints and it looks like the guy who did the install did a good job. No splits, cuts, burrs or any of that. When I put the flares back together I put a little pro-dope on them since I couldn't think of anything better to do besides tighten them down as best as I could. I changed the filter and gaskets and that seemed to take care of the leak on the filter.

    Here are my questions:
    Is there anything about kerosene that would make it leak more than #2 fuel oil? It seems a little thinner than #2 and I thought it may leak in colder conditions. Kinda the way PEX piping can leak a little when it's cold. The basement was chilly, maybe in the 50s. Or could it sneak its way through the threads if there wasn't any thread dope?

    Was my thread dope idea ok? Some guys like the stuff and some guys don't. What's your take?

    Thanks
    You should never put any type of teflon based sealants on flare fittings.
    A flare fitting is designed to have a copper/brass connection, like a union. Any impurity that gets lodged between the flare face and the male flare has the possibility of leak.

    It's like applying pipe dope to the face of a union. It's wrong, and is asking for problems.

    Teflon is for threaded pipe, and very specific applications.

    Second, what the heck is kerosene doing in a furnace?
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #3
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    I agree with hvacvegas on the use of any dope/tape on flares.

    kerosene, or #1, is used in place of #2 if the tank is located outside, someplace where #2 would gel/freeze.

    if tank is in the house/basement it should not need #1, #2 should be fine.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  4. #4
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    ^ agree with previous postings, flares and unions can be lubricated with oil, zoom spout in my case, so that the surfaces don't "catch" or warp during tightening.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Yep, flare connections are metal to metal seals, no dope or sealant is required, nor should be used. Look for under or over flared ends.

  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by pacnw View Post
    I agree with hvacvegas on the use of any dope/tape on flares.

    kerosene, or #1, is used in place of #2 if the tank is located outside, someplace where #2 would gel/freeze.

    if tank is in the house/basement it should not need #1, #2 should be fine.
    Back in my oil days, I had several customers with outside tanks who ran #2.

    Most of my kerosene customers were in mobile homes.

    Apparently, there is a choice of nozzles and perhaps combustion chambers that are used for kero, and other choices for use with #2. You can cut #2 with some kero in really low temps to reduce gelling, but more frequently, we would offer a bottle of additive to control gelling.

    That was 20 years ago, when we used to get some pretty cold winters in this part of the country. A 3° overnight temp was not unusual. For the past decade or so, I can't remember a 3° night.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Last winter we had a -6°F temp one of the mornings.

    I go back a bit further to the 70s, and remember when it was normal to have 2 weeks of 0 and colder weather every winter. Kerosene was put in all outdoor tanks then by most people. those who tried to save a couple dollars by only getting #2, ended up spending that money plus by paying for a service call, and a few gallons of kerosene to be added to thin it down to get the tank to thin out.

    Even had to remove a line or 2, and thaw it in my truck. But never any problems with the flare fitting leaking because it was kerosene instead of #2.

  8. #8
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    The flare should should be air tight, which would mean liquid should not flow trough. On any union or flare oil is the best even in compression fittings.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by beenthere View Post
    Last winter we had a -6°F temp one of the mornings.

    I go back a bit further to the 70s, and remember when it was normal to have 2 weeks of 0 and colder weather every winter. Kerosene was put in all outdoor tanks then by most people. those who tried to save a couple dollars by only getting #2, ended up spending that money plus by paying for a service call, and a few gallons of kerosene to be added to thin it down to get the tank to thin out.

    Even had to remove a line or 2, and thaw it in my truck. But never any problems with the flare fitting leaking because it was kerosene instead of #2.
    Wow, what a difference that 50 miles can make. We never went below 5° last year that I saw.

    I loved the in-ground tanks with a two line setup. Nearly trouble free.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by timebuilder View Post
    Wow, what a difference that 50 miles can make. We never went below 5° last year that I saw.

    I loved the in-ground tanks with a two line setup. Nearly trouble free.
    Yep, no muss no fuss.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •