I am relaying this issue from my very experienced tech.
reversing valve on a goodman R22 HP has been failing at cap-pilot connection, either at hot gas or suction.
4 and counting.
Goodman has suggested many solutions, all followed but no inprovements.
No vibration seen, no slugging, new compressor with looped hot discharge to absorb vibration.
Anyone Seen this?
11-21-2012, 07:38 AM #2
- Join Date
- Oct 2002
- Posts
- 715
Wow. No one has an idea?
11-21-2012, 08:41 AM #3
11-21-2012, 08:53 AM #4
- Join Date
- Oct 2002
- Posts
- 715
Would have if it wasn't R22. Goodman warranty some valves.
11-21-2012, 09:27 AM #5
I understand the valve is under warranty, but are you eating the labor to do all that or is the customer?
4 reversing valves and a new compressor and it's still blowing the cap tube..... hmmm
Did this just start since the heating season?
11-21-2012, 09:40 AM #6
- Join Date
- Oct 2002
- Posts
- 715
No heating here yet!
Not sure, but I think been dong it since last year.
Not customer.
11-21-2012, 09:44 AM #7
- Join Date
- Oct 2002
- Posts
- 715
4 times since 2008
11-21-2012, 09:51 AM #8
So the info is from your tech, but it's not your customer.....
Step in and sell them a new unit.
11-21-2012, 10:16 AM #9
- Join Date
- Oct 2002
- Posts
- 715
my customer. Unit was new when problem started
11-21-2012, 12:36 PM #10
Chinese Kwality
12-02-2012, 04:16 PM #11
Professional Member
- Join Date
- Apr 2005
- Location
- AZ
- Posts
- 181
I've only had one unit that busted a pilot tube more than once. 2 times within a couple months or something like that. I went out to do the 2nd and found poor connection causing a chatter. Can't remember if it was contactor or valve chattering but it took care of it. It was a 410 unit but...