    Purpose of two way modulating valve at chiller

    Hi, Can anybody tell me purpose of using 2 way modulating valve at chiller. Its 2 chillers( 1 W+ 1 S ) connected to common header. Where should it be connected, supply or return?
    Is it required at condenser side also?

  2. #2
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    It's probably there to maintain design flow through the chiller. It should be on the leaving side of the chiller.

  3. #3
    Join Date
    Nov 2012
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by R123 View Post
    It's probably there to maintain design flow through the chiller. It should be on the leaving side of the chiller.
    Its a constant primary flow chiller and Design CHW flow through evaporator is always maintained by the primary pumps. Also Balancing valve provided at the chiller outlet for flow balancing.

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    Are you certain it is a modulating valve and not an isolation valve? One isolating valve is all that is needed to isolate if the goal is to stop flow through an idle chiller.

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    And what does "1 W+ 1 S" mean?

  6. #6
    Join Date
    Nov 2012
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by R123 View Post
    It's probably there to maintain design flow through the chiller. It should be on the leaving side of the chiller.
    its 1 working + 1 standby, Its not motorized isolation valve..

  7. #7
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,042
    Post Likes
    But are you certain it is a modulating valve? Have you watched it modulate? if so, what did it appear to be responding too? Hopefully there are control prints somewhere on site. They would be able to provide an answer. Also what operates the valve? A pneumatic actuator? An electric motor? An isolation valve or a modulating control valve could use either type of actuator.

  8. #8
    Join Date
    Mar 2004
    Location
    Windsor ON Canada
    Posts
    424
    Post Likes
    I believe it could be used to provide a constant delta T across chiller barrel, regardless ol load by varying the flow. There would be limits based on minimum and maximum allowable flow thru the chiller to maintain acceptable velocities. I can think of one existing chiller company which uses this and VFD compressor control for maximum energy conservation.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •