11-18-2012, 09:02 PM #27
Regular Guest
- Join Date
- Nov 2012
- Location
- Arlington, TX
- Posts
- 11
Thanks everyone for the suggestion. Ohmed out all the wires and couldn't find a short. Going to run new wire to the thermostat. Had tried a new thermostat, thought that may have been the problem, but it didn't solve it.
-
11-18-2012, 09:19 PM #28
I like in situations like this to start wiggling wires while the power is off. Especially where it penetrates thru walls and the unit cabinet.
-
11-18-2012, 09:19 PM #29
Professional Member
- Join Date
- Jun 2012
- Location
- Fayetteville, NC
- Posts
- 117
did you disconnect the t stat wires and check for shorts? I'd ohm out some the components you haven't changed i.e coils
-
11-19-2012, 12:22 AM #30
Regular Guest
- Join Date
- Nov 2012
- Location
- Arlington, TX
- Posts
- 11
Very last thing I checked was the t-wire. Isolated it from the system. Nothing. Replaced thermostat. changed the control box with one rebuilt with all new components (I work in a apartment community so I have the spares ready to swap-out). Got to be the wire. It's the only thing that hasn't been changed. I have another apartment's air handler doing the same thing. Fortunately, it's vacant and I suspect whatever is causing this issue is going to be the same problem.
-
11-19-2012, 05:43 AM #31
Hope your not using doorbell transformers.
-
11-19-2012, 07:14 AM #32
Professional Member*
- Join Date
- Oct 2002
- Posts
- 675
Think this out. Older systems do not usually have a "common" wire run to the stat. Short the wires, what do you have?
CU wire short, blows only on cool call.
Did poster say primary is blown, check 208/230 volt tap is correct. Is "common" conductor in stat cable run?
-
11-19-2012, 07:54 AM #33
Regular Guest
- Join Date
- Jun 2001
- Location
- Moore, Oklahoma
- Posts
- 2,596
-
11-19-2012, 07:56 AM #34
Regular Guest
- Join Date
- Jun 2001
- Location
- Moore, Oklahoma
- Posts
- 2,596
Had one where the tstat wire was ran across a roof w/o conduit. The sun dryrotted the insulation and it shorted when it rained.
-
11-19-2012, 08:34 AM #35
Professional Member*
- Join Date
- Oct 2002
- Posts
- 675
It is possible that "R" is grounding to a water pipe, but transformer winding has to be connected to ground on "C" side.
-
11-19-2012, 09:15 AM #36
Professional Member
- Join Date
- Jun 2012
- Location
- Fayetteville, NC
- Posts
- 117
Ohm out all your coils inside and out, if one has low resistance that may be it. Low resistance through a coil is basically a short since there is little to no load
-
11-19-2012, 09:35 AM #37
Professional Member*
- Join Date
- Nov 2012
- Location
- Tahlequah OK
- Posts
- 131
Is this a heat pump? I have had contactor 24 v coils in the heat pump or condenser do this. They are just beginning to go to ground and are very erratic. Some of them would run for a while before blowing the fuse.
-
11-19-2012, 08:44 PM #38
Regular Guest
- Join Date
- Nov 2012
- Location
- Arlington, TX
- Posts
- 11
Turns out that this was the problem, along with a lot of other spaghetti wiring that the previous maintenance tech had done. Had the thermostat wired for a heat pump. Had to call out the original contractors to come out and look at it. Thanks every one for your help. I am new to the game and learning. BTW, it turns out the the blower motor was wired to run 240v for both cooling and heating, he fixed that as well. You guys rock. Have a blessed thanksgiving...
-
11-19-2012, 11:20 PM #39
Professional Member*
- Join Date
- Nov 2012
- Location
- Tahlequah OK
- Posts
- 131
miscand the blower uses 240VAC in both modes. The difference is motor speeds. It is lower in heating mode.