Results 14 to 26 of 39
-
11-16-2012, 09:19 PM #14
Regular Guest
- Join Date
- Aug 2012
- Location
- NE wisconsin
- Posts
- 178
-
11-16-2012, 09:34 PM #15
I like the multi fuse idea to narrow down cause.
Col 3:23
questions asked, answers received, ignorance abated
-
11-16-2012, 11:22 PM #16
Professional Member
- Join Date
- Jun 2012
- Location
- Fayetteville, NC
- Posts
- 117
I ran into something similar a few weeks ago, went through 3 transformers before i finally wised up and asked a senior tech.
-
11-16-2012, 11:59 PM #17
If I am blowing transformers I just don't put another one on until I find out whats making my VA to high. Chances are its cause someone took a 75VA off and replaced it with a 50VA.
If you're too "open" minded, your brains will fall out.
Artificial intelligence is no match for natural stupidity.
-
11-17-2012, 12:44 AM #18
I always carry a transformer with a built in circuit breaker when i come across a bad transformer... I use it as a troubleshoot aid
-
11-17-2012, 02:43 AM #19
Professional Member
- Join Date
- Aug 2009
- Location
- Las Vegas
- Posts
- 37
Just check your wires for a short
-
11-17-2012, 09:39 AM #20
Is it blowing on the primary or secondary side?
-
11-17-2012, 09:52 AM #21
Get some fuses and get your post count up
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
11-17-2012, 10:37 AM #22
Regular Guest
- Join Date
- Nov 2012
- Location
- Arlington, TX
- Posts
- 11
-
11-17-2012, 02:02 PM #23
Professional Member
- Join Date
- Nov 2008
- Location
- DFW,TX
- Posts
- 1,891
use a resettable in line fuse until you find the issue and make sure you check anything and everything related to the low volt system, sounds like a bare 24 v wire that is rubbing on metal or another bare wire next to it that goes common..Ive found many outside in the condenser cabinet especially on heat pumps where the wires have been tied to copper pipes eventually rubbing through.. keep looking and you should find it , id say look at running new aire from stat to AH as its happening in heat and cool or its in the Tstat itself..
-
11-17-2012, 03:42 PM #24
You have a direct short. Ohm out all wires and isolate.
-
11-17-2012, 03:56 PM #25
Yep sounds like a direct short as already stated. I had the same problem a few months back. I put a Lil' Popper in and blew probably 12 fuses before I found it. It was an older house with terrible wiring. When I finally found the problem, someone had spliced wires about 15 feet from the panel and just taped it up with electrical tape. I assume they didn't have enough wire to finish the run, but that didn't make me any less upset. The house could've very easily burnt to the ground.
-
11-17-2012, 10:35 PM #26
Professional Member
- Join Date
- Dec 2009
- Location
- Union Nj
- Posts
- 23
I had this issue, in ny a rat chewed on the tstat wire and shorted every time. Just need to ohm wires.



Reply With Quote