11-18-2012, 04:13 AM #27
Timebuilder I have wondered this for some time now - about the seperate neutral 4 wire range and dryer cords.
I understand what you mean about not using ground as current path.
At the dryer electrical connection there is a jumper from ground to neutral so what did this really accomplish?
-
11-18-2012, 07:34 AM #28
The intention of that equipment jumper was to place the chassis of the dryer at the same potential as the "grounded conductor," which we routinely call the "neutral" conductor.
(Note: the NEC refers to the "hot" wires as the "ungrounded" conductors, the neutral as the "groundED conductor, and the ground wire as the "groundING conductor. They are working on changing the verbiage for most grounding conductors to BONDING conductors, since the purpose of an Equipment Grounding Conductor is to "bond" the metal parts to the panel via wires and conduit so that any short results in the overcurrent device being opened, which cuts off power to the offending appliance.)
Today, we use a separate conductor that is intended to carry NO current unless there is a fault, and that is the fourth wire. It eliminates the possibility that the cabinet can become energized due to neutral currents in the circuit. This raises the level of safety, which is what the code is all about.
Does that help?[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
11-18-2012, 07:43 AM #29[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
11-18-2012, 11:14 AM #30
Regular Guest
- Join Date
- Jan 2012
- Location
- Fresno, ca
- Posts
- 30
-
11-18-2012, 11:34 AM #31[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
11-18-2012, 11:57 AM #32
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 878
-
11-18-2012, 07:34 PM #33
-
11-18-2012, 08:04 PM #34[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
11-18-2012, 09:32 PM #35
Regular Guest
- Join Date
- Jan 2012
- Location
- Fresno, ca
- Posts
- 30
I ohmed the new motor right out of the box. The motor only has 3 leads, black, yellow and brown. I just checked from one lead to another. I checked the old motot the same way, with the motor leads off.
I guess there is a chance my meter was wrong, but I ohmed a different motor the same day because I wanted to compare numbers and it was about right. The only difference was the voltage. The old and new motor were 460 single phase. The compared motor was 208/240 single phase.
I knew somthing was up...
-
11-19-2012, 06:03 AM #36[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
11-19-2012, 06:09 AM #37
A single phase motor that uses a run cap has three wires, and two windings. One is a run winding, and the other is usually referred to as an "aux" winding, which has a function similar to a start winding. The brown wire goes to the aux winding.
What readings did you measure?[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
12-08-2012, 03:13 PM #38
Professional Member
- Join Date
- Jan 2008
- Location
- Hells Kitchen, Phoenix Arizona
- Posts
- 318
Essentially Black is common, Yellow is run, and Brown is start...Brown to yellow "Should" have the most resistance. Black to Brown the second highest, and Black to yellow the least...A volt meter can pick up on a shorted motor, a grounded motor is a different animal...A short is a broken wire...A ground is a crack in the lacquer in the windings causing power to "leak" to ground...You need meg-ohm meter for that...The OP got blasted by a grounded motor, a shorted motor would blow the fuses or the breaker...

BTW most of this is my experience, there is no hard fast rule on wire colors, the schematic or hook up diagram doesn't lie..."Overkill is an often underrated achievement", Will Hayden -- Red Jacket Firearms
-
12-08-2012, 08:19 PM #39
Couldn't agree more R123.
Mechs who rely on a multimeter to test resistance to ground (earth) run the risk of killing themselves or worse, their paying customer.
Here are a couple of links of links to the type of meters we're talking about:
http://www.hioki.com/product/field.html
http://www.myflukestore.com/c538/meg...p?currency=USD
They may be expensive but how much is your life worth to you and your family?Mistakes are a part of being human. Appreciate your mistakes for what they are: precious life lessons that can only be learned the hard way. Unless it's a fatal mistake, which, at least, others can learn from. Al Franken, "Oh, the Things I Know", 2002