Results 1 to 11 of 11
    May 2003
    El Paso, TX
    Hmm Compressor overload opening after 20 minutes?
    Am. Std. CU- M# TTA120A400BC S# N3146DHAH
    A/H M# TWE120A300CA S# N27105E5H
    Compressor overload opening after 20 minutes of operation; ambient 85
    Suc.- 63 psi @39 SAT
    line temp 69 SH 30
    Liq.- 212 psi @ 106 SAT
    Line temp 96 SC 10
    Sup 65 Ret 78 WB 69
    COOL
    oklahoma city
    What is the amp draw? The overload will open if the current is to high. It could be any of the electrical components, or wiring, that are causing your problem.
    Edit: I re-read the rules, and might not be allowed to post, but the question was asked by an authorized Pro, and my advise was vague...??? Delete if I'm breaking the rules.
    NW AR
    Yea you need to check your amp draw. Your pressures are temps are fair. Possibly run capacitor. If unit has a start capacitor that will get it running but if the run is bad it will be over amping and getting hot.
    Dec 2003
    Northern VA
    How is the oil doing?
    "Iron sharpeneth iron..."
    May 2003
    Charleston SC
    Check the contactor, if the contacts are bad you can get a current imbalance between phases in the compressor motor-causing overheating.
    Coolairman
    Jun 2008
    Seems like you're low on charge or have a restriction. SH of 30 is a little high. With those readings, your target SH should be about 19 degrees. SH too high will make the compressor run hot. Also check your temp split across your liquid drier to make sure there's no restriction. If it has a txv see what happens if you bring your SC up to 15
    Jul 2009
    Columbia, MD
    I agree with him ^^^
    High superheat will cause an overload. That unit is most likely a TXV. See if you can check pressure drop across the drier. Trane uses a small drier which will clog up.
    Nov 2009
    Richmond, working under tarps
    Quote Originally Posted by dukes13 View Post
    line temp 69 SH 30
    Line temp 96 SC 10
    Sup 65 Ret 78 WB 69
    Is the return gas temp at compressor 69deg F?
    May 2003
    El Paso, TX
    It was a TXV restriction, tkx for replys.
    COOL
    txv and tkx's im so confused.
    Glad it worked out.