Results 1 to 7 of 7
  1. #1
    Join Date
    Mar 2005
    Location
    Georgia
    Posts
    426
    Post Likes

    Niagara AX Andover integration

    What if any drivers are available to talk to infinity field controllers? I think I remember a 232 driver that allows integration through the big orange main panel. I really don't wanna go that route. I have a special place in mind for that big orange antique.

  2. #2
    Join Date
    Nov 2012
    Posts
    10
    Post Likes
    The only way I know of communicating to the field controllers is with the Infinity Driver offered. It does not integrate directly to the field bus. It relies on a serial connection to the andover "big orange main panel" to communicate to the system just as you would with hyperterminal. It definately has it quirks, but it may be the best of whats available.

  3. #3
    Join Date
    May 2011
    Posts
    5
    Post Likes
    I think that you can use a BCX to convert from Infinet to Bacnet.

  4. #4
    Join Date
    Mar 2005
    Location
    Georgia
    Posts
    426
    Post Likes
    Thread Starter
    Quote Originally Posted by matcai View Post
    I think that you can use a BCX to convert from Infinet to Bacnet.
    Hmm I will look for some more info on this BCX.

  5. #5
    Join Date
    Mar 2007
    Posts
    299
    Post Likes
    Quote Originally Posted by matcai View Post
    I think that you can use a BCX to convert from Infinet to Bacnet.
    a bCX will not work on a Infinet bus... it only works with a Bacnet MSTP bus

  6. #6
    Join Date
    Mar 2005
    Location
    Georgia
    Posts
    426
    Post Likes
    Thread Starter
    Quote Originally Posted by exwtk View Post
    a bCX will not work on a Infinet bus... it only works with a Bacnet MSTP bus
    Ok, that was the conclusion I was coming to as I was looking through the literature. Well that just sucks! I can't believe driver developer don't have something to talk directly on the 485 field bus. Anybody have experience using the current tridium Infinity driver that talks to the AC256? Will it discover field devices, and all points connected to the AC256?

  7. #7
    Join Date
    Dec 2011
    Location
    Charlotte, NC
    Posts
    47
    Post Likes
    As a worst-case scenario, could you use a NetController II to convert from InfiNet to BACnet? I saw worst case because I'm guessing that thing is not cheap...

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.