    Confused Carrier 19DH chiller

    Good day.
    Can anyone tell me why there are 2 Refrigerant sight glasses on the 19DH Carrier Chiller?

  2. #2
    Join Date
    Mar 2011
    Location
    Abilene Tx
    Posts
    82
    Not real sure about your unit you got there. But I would think something like one is for unit shutdown refrigerant level and the other while unit has been running. To determine proper charge. Call Carrier and look in IOM.

  3. #3
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    873

    Sight glasses on a 19DH

    Ruol- They had them on special blue light sale that year at K-Mart.-GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  4. #4
    Join Date
    Aug 2010
    Location
    Memphis
    Posts
    343
    depends where they are at

  5. #5
    Join Date
    Mar 2011
    Posts
    254
    Actually I thought it was the 19DG that had the sight glasses? My memory is fading, but...

    They use two sight glasses instead of using one really large one. The level has a range that is acceptable, and the level will change with different operating conditions. As long as it's visible in either glass your fine. Also you should only use this as a guide, you still need to check approach, discharge superheat and water flows to get the full picture.

  6. #6
    Join Date
    Jan 2008
    Location
    windy city
    Posts
    4,423
    Quote Originally Posted by ga1279 View Post
    Ruol- They had them on special blue light sale that year at K-Mart.-GEO
    \m/
    original member of the racoon brotherhood

  7. #7
    Join Date
    Dec 2010
    Location
    georgia
    Posts
    83
    I found these sight glasses very useful, I miss them on newer machines.
    I agree with Chiller Man about approach,but to me there is nothing like seeing
    where level acually is. Hard to detemine sometimes with just one sightglass.

  8. #8
    It almost all comes down to pressures and temperatures. Obtain all your Approaches, Condenser, Cooler and yes, Cooling Tower. Get all of your Delta Ps and Delta Ts. Check your Discharge SuperHeat. Always consult with your manufacturers with that one because some factor with Saturated Condensing Temperature from the Discharge Line Temperature and some factor with Saturated Discharge Temperature from the Discharge Line Temperature.

  9. #9
    Join Date
    Dec 2013
    Posts
    6
    In the manual it says something about the bottom sight glass is for checking charge when the unit is not running and i think the top one is just kinda of a way to see in when the unit is running to see the refer going over the tubes.