Results 1 to 9 of 9
    Nov 2012
    Trane screw chiller
    Alarm indicates a low refrigerant liquid level in circuit #2, however my subcooling is 20F. The rest of my readings show:
    EXV 100% OPEN
    Liquid level (-1.7)
    Evaporator pressure 27.8
    Evaporator approach 11.8
    Condenser pressure 125
    Condenser approach 16
    Discharge superheat 42.5
    Sight Glass (NO bubbles)
    Liquid line filter drier (No temperature differental)
    Leaving chill water: 44F
    Entering chill water: 60F
    Any idea what it could be? I suspect it is a refrigerant restriction somewhere mabye in the EXV, but I was able to see the stem of the EXV move in and out. Could the EXV still have a restriction but be mechanicaly ok?
    The Hot South
    It would help if you posted the model and serial number....
    Is this the RTWD100 chiller Serial # U08L02012 in Hawaii?
    Also, where are you taking your temperature and pressure readings to determine subcooling?
    Not in Iran
    Ur exv should not be 100% open -/ remember that ur chiller wants to stay running no matter what ,. Low liquid level- ur -1.7 is not correct at all,. Should maintain 0.0
    In condenser and evap,.I would be looking for oil residue /- also u might want to think about weighting the charge. And ur approach is way out of wack- u have a few things going on here,. Could very well be dirty tubes
    this sounds a touch familiar! this thread is in the pro chillers sections where this tech can't look...competing companies on the same job?
    Not in Iran
    Really.,/- well hope they get it squared away
    Might see theses guys in the octagon going toe to toe.,
    Can I have ring side seats
    Quote Originally Posted by milkyway View Post
    ...Can I have ring side seats
    i will sit next to you! you get the popcorn i'll get the beers!
    A land down under
    Well worth the price of ringside seats if the Canadian Crusher joins the stoush!
    Nov 2012
    I was able to override both circuit EXV's to open 100% and compared the two. The one that im working on only open up 50% when looking through the sight glass while the other one looks like a 100% open. Tried banging it with a wrench to see if it was stuck but that did not work. Gonna change out the EXV motor. You guys are funny!
    Nov 2012
    Increased1