    The heat pump is a 19KW , water to water
    - on low pressure side we have: inlet water 16C, outlet water 12C, pressure of the refrigerant 4.5 bar
    - on high pressure side: inlet water 30 C, outlet water 35 C, pressure of the refrigerant is 20 bar
    This high pressure is to high for the 35 C water outlet
    The top of the compressor is 70C, too hot
    If the water outlet is set 40 C we have pressure error (compressor stops)
    We recharge the heat pump with R407C, the qty is correct. But the pressures are still to high
    When we open fully the expansion valve the low pressure rich 5.5 bar and high one 18 bar / the top the compressor is still 70C
    Nov 2011
    Who said 70˚C is too hot or 20 bar too high?
    Nov 2011
    20bar is to much for 35c water outlet ...
    Nov 2011
    Quote Originally Posted by housed View Post
    I'm not intimately familiar with water source coil applications, but if it's too high, I'd think the problem is over-charge or reduced condensing. Those are usually the causes. Did you measure superheat and subcooling?
    You know what the condensing temp is supposed to be, relative to the water temp?
    Nov 2011
    Subcooling is 27 k ...
    Normal condensing presure is around 15
    QUOTE=Saturatedpsi;14617201]I'm not intimately familiar with water source coil applications, but if it's too high, I'd think the problem is over-charge or reduced condensing. Those are usually the causes. Did you measure superheat and subcooling?
    You know what the condensing temp is supposed to be, relative to the water temp?[/QUOTE]
    Nov 2011
    27 k?
    How much in Fahrenheit?
    20bars=290PSIG, 4.5bars=65PSIG.
    70C=158F.
    27K SC = 48.6F of subcooling.
    Nov 2011
    That seems like a lot of excess subcooling to me for a high temp application.
    Only has a 7F water delta across the evap, and 9F on the condenser.
    R407C at 290PSIG is a sat of 118F, and at 65PSIG is a sat of 42F.
    Chance of a restriction in refrigerant circuit.
    Nov 2011
    We made a cleaning with acid solution of the condenser and the situation is back to normal, pressure 16