11-15-2012, 11:36 PM #40
I would go back over that HX install again with a fine tooth comb.
I know the burners have a particular way they lay on each other that might be another thing to check, along with alignment in the opening.
Gravity might have already sent it too you, but I'll email you a pdf of how they go together.Instead of learning the tricks of the trade, learn the trade.
-
11-16-2012, 05:54 PM #41
Regular Guest
- Join Date
- Sep 2007
- Location
- Nashville,Tn
- Posts
- 30
That was the problem!!! The inducer draft motor was wired wrong. I had the brown where the purple should be! Changed these two wires and it fixed it!
-
11-16-2012, 07:37 PM #42
Glad you found and resolved the issue. I still want to know how the CO levels rose in the building
Sent from my HTC Sensation 4G using Tapatalk 2
-
11-17-2012, 12:56 PM #43
Regular Guest
- Join Date
- Sep 2007
- Location
- Nashville,Tn
- Posts
- 30
Me too! I was thinking about that myself!
-
11-17-2012, 01:26 PM #44
So, your inducer was spinning backwards?
-
11-17-2012, 04:00 PM #45
Professional Member*
- Join Date
- Mar 2010
- Location
- Arnold, Mo
- Posts
- 283
-
11-17-2012, 04:53 PM #46
http://www.carrierenterprise.com/
On the bottom right of the page.
Sent from my HTC Sensation 4G using Tapatalk 2
-
11-17-2012, 05:02 PM #47
Professional Member*
- Join Date
- Mar 2010
- Location
- Arnold, Mo
- Posts
- 283
-
11-18-2012, 12:22 AM #48
Your welcome. I hope you find it useful. That app prevented me from being 2 hours away with the wrong parts.
Sent from my SCH-I800 using Tapatalk 2
-
11-19-2012, 08:51 AM #49
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,640
-
11-19-2012, 04:57 PM #50
-
11-28-2012, 11:14 AM #51
Ran a call the other day identical to this thread. Odor was strong with CO levels around 15ppm. Heat exchanger was ok and draft motor rotating the right way. No economizer package to allow extra infiltration. Long story short gas valve inlet 7.9 outlet 6.0. Natural gas. Replace valve all good. The previous response to my question sunk in much more after this call
Sent from my SGH-T999 using Tapatalk 2


Reply With Quote