    I have a Trane xl15i heat pump, an XV80 natural gas furnace and a Trane TCONT803 stat with dehumidify feature. I have my heat pump lockout set at 25.

    My natural gas service is currently turned off. I monitor the forecast and when I see it is going to get bitter cold I will call and have it turned on. I didn't have it turned on until mid January last year and then didn't need it that much. I save a little by only having my natural gas turned on 2-3 months a year and my local utility does not charge a connection fee if it has been off for 8+ months.

    I've noticed a few times recently where the heat pump fan stops and the heat pump makes a buzzing noise. I assume this is a normal defrost cycle. When this was happening I measured the temperature coming out of my registers at 40 degrees (I have black and decker thermal leak detector). This was happening for several minutes. The heat was set at 70 but had dropped to 66 when this happened over just a few minutes. This was with outside temperature of 27 shown on the stat and normal heat mode (not aux heat). Is this the expected behavior? Should my furnace fan turn off during the defrost cycle to prevent my house from being cooled?

    thanks for any help with this...

  2. #2
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    It sound normal, and no the indoor fan should not shut off. Its taking the heat from the home to defrost the outdoor coil.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  3. #3
    Join Date
    Aug 2010
    Posts
    19
    Post Likes
    Thread Starter
    that makes sense, thanks for the help

  4. #4
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    If the gas was turned on the furnace would kick on during defrost so you wouldn't have 40 degree air.

  5. #5
    Join Date
    Aug 2010
    Posts
    19
    Post Likes
    Thread Starter
    When it was blowing cold air I was still on heat, not aux heat.

  6. #6
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by supermaxhd View Post
    When it was blowing cold air I was still on heat, not aux heat.
    When any heat pump goes into defrost it temporarily goes back to "AC mode". The only difference between defrost and AC is the fan doesn't run outside. To offset the cooling effect of the AC running, the defrost board in the outdoor unit will turn on the AUX heat. If gas isn't turned on your AUX heat won't run, therefore you will have cold air out of the registers.

  7. #7
    Join Date
    Aug 2010
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    When any heat pump goes into defrost it temporarily goes back to "AC mode". The only difference between defrost and AC is the fan doesn't run outside. To offset the cooling effect of the AC running, the defrost board in the outdoor unit will turn on the AUX heat. If gas isn't turned on your AUX heat won't run, therefore you will have cold air out of the registers.
    Gas heat would have kicked in just for the few minutes for the defrost cycle and then return to heat pump after the defrost cycle even though the outside temperature was not low enough for the heat pump lockout setting to kick in the gas heat?

    My house is small and tightly insulated. I am on monthly electric budget plan for $79 right now. I will have my natural gas turned back on after November 26 when it can be turned on without a reconnect charge.

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Have you considered just getting rid of gas altogether and running electric for backup heat? I understand the want to get rid of that gas meter fee, it's $28/mo for us with a 12 month cutoff agreement instead of the 8 you have. Our reconnect charge is the $28/mo for all the months you missed !!!

    Yes, your defrost board should kick the furnace on for a few minutes while your heat pump defrosts. Exact sequence of operation depends on how the duel fuel kit was wired.

  9. #9
    Join Date
    Jan 2009
    Location
    Saint Joseph, MI
    Posts
    5,564
    Post Likes
    I found with my XV80 and XL16i combo at my last home, that by the time the furnace actually warmed the HE and produced any heat, the defrost cycle was over anyway. Still better than nothing. In a perfect world, there would be a dual fuel defrost mode that had a a time delay once defrost is "requested" by the condenser to give it time to fire up the furnace.

  10. Likes DavidDeBord liked this post
  11. #10
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    3,889
    Post Likes
    I have my heat strips off. The little time it is in defrost doesn't bother me and saves. Heat strips use alot of watts. I realize they are only on briefly but still a little savings.

  12. #11
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,065
    Post Likes
    what is needed is a duct heater used during defrost
    Go Trump

  13. #12
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,217
    Post Likes
    Quote Originally Posted by catmanacman View Post
    what is needed is a duct heater used during defrost
    Duct heater = ELECTRIC STRIPS.!

    LOCATION?
    degreedays dot net will assist in determining
    1. how many weeks natural gas would be needed.
    2. if last year was atypical or not.

    How much gas did you use last year?
    Conversion to electric should be investigated.
    For example,
    100 therms =~ $100. natural gas.

    100 Therms
    100,000 BTU per hr/ therm
    10,000,000 BTU/Hr
    3412 BTU per Hr/ kW
    2931 kW
    $0.09 $ / kw or YOUR Rate
    $263.77 electric strip backup
    $100.00 N.Gas
    $163.77 extra over Natural Gas
    or
    __50 therms
    $ _50 N. Gas
    $ 131 electric
    $ _81 extra for electric strips over N. Gas
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  14. #13
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    8,217
    Post Likes
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.