    Confused Trane Voyager Condenser Fan Problems

    So i replaced a condenser fan motor capacitor and fan blade on a Voyager Rtu and when i fired it up the motor was spinning backwards, its a single phase motor, so i was alittle puzzled, i called Trane and they were alittle confused as well, suggested i swap the wires from the contactor and capacitor, motor was then spinning correctly but drawing about 1.5-2 amps higher than what it was rated for. So bottom line getting a new motor and capacitor from trane and trying it again. Just wondering if anyone has had anything similar to this?

  2. #2
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,120
    Post Likes
    Was it a 3 wire fan motor?
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  3. #3
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    If there are 2 fans
    The second one can start backwards.

  4. #4
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    Ive seen it.

  5. #5
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Quote Originally Posted by supertek65 View Post
    Ive seen it.
    X2

  6. #6
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    What is the Model Number of the RTU?

  7. #7
    Join Date
    Nov 2012
    Posts
    3
    Post Likes
    Thread Starter
    There is 2 compressors, and 1 condenser fan, the mod number was YCD120C4L0AB....and it was 3 wire motor Trane suggested swapping the black wire on the contactor with the purple wire off the cap and it seemed to correct the problem other than the high amp draw and the door was on the unit lol.

  8. #8
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Double check the motor, cap and blade, just cause they're new, doesn't mean they're the correct ones, Trane makes mistakes too. Got a 208v compressor in a 460v box before. Didn't run very long.

  9. #9
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    798
    Post Likes
    Sounds like the motor is bad. I'm not sure if you replaced the motor, capacitor and blade or just the motor capacitor and blade. If it was a new motor, you got a bad one. I have purchased several motors from Trane that were bad out of the box or only lasted a day or two.

  10. #10
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,120
    Post Likes
    Quote Originally Posted by ErikNeMechnical View Post
    There is 2 compressors, and 1 condenser fan, the mod number was YCD120C4L0AB....and it was 3 wire motor Trane suggested swapping the black wire on the contactor with the purple wire off the cap and it seemed to correct the problem other than the high amp draw and the door was on the unit lol.
    Exactly what I thought and why I asked, I myself have done it more than once(we have a ton of Trane Voyagers around here) and that is the proper fix.

    Now on the high amp draw is the capacitor the same size? When you changed the fan blade did you put it in the same place?
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  11. #11
    Join Date
    Nov 2012
    Posts
    3
    Post Likes
    Thread Starter
    Yeah fan blade is in same place capacitor is good, just swapped the motor and cap with another new one and its working great now... Weird **** but atleast I don't feel to bad now that some of you guys have experienced this.

  12. #12
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Wound for opposite rotation. Factory mix up. It happens.

  13. #13
    Join Date
    Feb 2011
    Location
    Sacramento, CA
    Posts
    148
    Post Likes
    Quote Originally Posted by Sicofthis View Post
    Wound for opposite rotation. Factory mix up. It happens.
    What he said is true, had this happen to me before, got another new motor and magically it ran the right direction.
    I have done so much with so little for so long, that now I can do almost anything with nothing at all.

  14. #14
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    Post Likes
    Carrier 38AKS condensing units with 2 fans do this too. #2 fan rotates backwards while #1 runs, when #2 is energized, it continues to run in wrong direction. A new capacitor fixes this.....for a while!

  15. #15
    Join Date
    May 2000
    Location
    Salem, WI US
    Posts
    83
    Post Likes
    Quote Originally Posted by GoColts View Post
    What he said is true, had this happen to me before, got another new motor and magically it ran the right direction.
    Have to be careful with York Equipment they run condenser fans in reverse to maintain system head pressures.......usually 3phase equipment though....

  16. #16
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    Post Likes
    I have not seen that before, interesting. Must have a second contactor to run fan in opposite direction.

  17. #17
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    2,253
    Post Likes
    Quote Originally Posted by Sicofthis View Post
    Wound for opposite rotation. Factory mix up. It happens.
    maybe at the factory they put the rotor in the wrong way. could have tried flipping the rotor.

  18. #18
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by Betabass View Post
    Have to be careful with York Equipment they run condenser fans in reverse to maintain system head pressures.......usually 3phase equipment though....
    Now that's one I haven't run across. Do you have a model number on that?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  19. #19
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    412
    Post Likes
    i have had the trane motor run in reverse before, i flipped the fan blade to get them by untill the new motor arrived. not the best. high head, also had to run a sprinkler on the coil. great for roof leaks.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •