    Carrier 38AKS condensing units with 2 fans do this too. #2 fan rotates backwards while #1 runs, when #2 is energized, it continues to run in wrong direction. A new capacitor fixes this.....for a while!

  2. #15
    Join Date
    May 2000
    Location
    Salem, WI US
    Posts
    61
    Quote Originally Posted by GoColts View Post
    What he said is true, had this happen to me before, got another new motor and magically it ran the right direction.
    Have to be careful with York Equipment they run condenser fans in reverse to maintain system head pressures.......usually 3phase equipment though....

  3. #16
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    I have not seen that before, interesting. Must have a second contactor to run fan in opposite direction.

  4. #17
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    609
    Quote Originally Posted by Sicofthis View Post
    Wound for opposite rotation. Factory mix up. It happens.
    maybe at the factory they put the rotor in the wrong way. could have tried flipping the rotor.

  5. #18
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,259
    Quote Originally Posted by Betabass View Post
    Have to be careful with York Equipment they run condenser fans in reverse to maintain system head pressures.......usually 3phase equipment though....
    Now that's one I haven't run across. Do you have a model number on that?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  6. #19
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    223
    i have had the trane motor run in reverse before, i flipped the fan blade to get them by untill the new motor arrived. not the best. high head, also had to run a sprinkler on the coil. great for roof leaks.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event