    Confused Trane Voyager Condenser Fan Problems

    So i replaced a condenser fan motor capacitor and fan blade on a Voyager Rtu and when i fired it up the motor was spinning backwards, its a single phase motor, so i was alittle puzzled, i called Trane and they were alittle confused as well, suggested i swap the wires from the contactor and capacitor, motor was then spinning correctly but drawing about 1.5-2 amps higher than what it was rated for. So bottom line getting a new motor and capacitor from trane and trying it again. Just wondering if anyone has had anything similar to this?

  2. #2
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,050
    Post Likes
    Was it a 3 wire fan motor?
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  3. #3
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    If there are 2 fans
    The second one can start backwards.

  4. #4
    Join Date
    Mar 2012
    Location
    Georgia
    Posts
    21
    Post Likes
    Carrier 38AKS condensing units with 2 fans do this too. #2 fan rotates backwards while #1 runs, when #2 is energized, it continues to run in wrong direction. A new capacitor fixes this.....for a while!

  5. #5
    Join Date
    Sep 2004
    Posts
    13,930
    Post Likes
    Ive seen it.

  6. #6
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,268
    Post Likes
    Quote Originally Posted by supertek65 View Post
    Ive seen it.
    X2

  7. #7
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    What is the Model Number of the RTU?

  8. #8
    Join Date
    Nov 2012
    Posts
    3
    Post Likes
    Thread Starter
    There is 2 compressors, and 1 condenser fan, the mod number was YCD120C4L0AB....and it was 3 wire motor Trane suggested swapping the black wire on the contactor with the purple wire off the cap and it seemed to correct the problem other than the high amp draw and the door was on the unit lol.

  9. #9
    Join Date
    Oct 2011
    Posts
    43
    Post Likes
    Double check the motor, cap and blade, just cause they're new, doesn't mean they're the correct ones, Trane makes mistakes too. Got a 208v compressor in a 460v box before. Didn't run very long.

  10. #10
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,050
    Post Likes
    Quote Originally Posted by ErikNeMechnical View Post
    There is 2 compressors, and 1 condenser fan, the mod number was YCD120C4L0AB....and it was 3 wire motor Trane suggested swapping the black wire on the contactor with the purple wire off the cap and it seemed to correct the problem other than the high amp draw and the door was on the unit lol.
    Exactly what I thought and why I asked, I myself have done it more than once(we have a ton of Trane Voyagers around here) and that is the proper fix.

    Now on the high amp draw is the capacitor the same size? When you changed the fan blade did you put it in the same place?
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  11. #11
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    673
    Post Likes
    Sounds like the motor is bad. I'm not sure if you replaced the motor, capacitor and blade or just the motor capacitor and blade. If it was a new motor, you got a bad one. I have purchased several motors from Trane that were bad out of the box or only lasted a day or two.

  12. #12
    Join Date
    Nov 2012
    Posts
    3
    Post Likes
    Thread Starter
    Yeah fan blade is in same place capacitor is good, just swapped the motor and cap with another new one and its working great now... Weird **** but atleast I don't feel to bad now that some of you guys have experienced this.

  13. #13
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    916
    Post Likes
    Wound for opposite rotation. Factory mix up. It happens.