Trane screw chiller
Alarm indicates a low refrigerant liquid level in circuit #2, however my subcooling is 20F. The rest of my readings show:
EXV 100% OPEN
Liquid level (-1.7)
Evaporator pressure 27.8
Evaporator approach 11.8
Condenser pressure 125
Condenser approach 16
Discharge superheat 42.5
Sight Glass (NO bubbles)
Liquid line filter drier (No temperature differental)
Leaving chill water: 44F
Entering chill water: 60F
Any idea what it could be? I suspect it is a refrigerant restriction somewhere mabye in the EXV, but I was able to see the stem of the EXV move in and out. Could the EXV still have a restriction but be mechanicaly ok?
-
11-15-2012, 12:26 AM #2
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 928
It would help if you posted the model and serial number....
Is this the RTWD100 chiller Serial # U08L02012 in Hawaii?
Also, where are you taking your temperature and pressure readings to determine subcooling?
-
11-15-2012, 07:25 AM #3
Ur exv should not be 100% open -/ remember that ur chiller wants to stay running no matter what ,. Low liquid level- ur -1.7 is not correct at all,. Should maintain 0.0
In condenser and evap,.I would be looking for oil residue /- also u might want to think about weighting the charge. And ur approach is way out of wack- u have a few things going on here,. Could very well be dirty tubes
-
11-15-2012, 09:22 AM #4
this sounds a touch familiar! this thread is in the pro chillers sections where this tech can't look...competing companies on the same job?
Time to get my nerd on!
-
11-15-2012, 09:35 AM #5
Really.,/- well hope they get it squared away
Might see theses guys in the octagon going toe to toe.,
Can I have ring side seats
-
11-15-2012, 09:16 PM #6
-
11-15-2012, 10:15 PM #7
Professional Member
- Join Date
- Sep 2008
- Location
- A land down under
- Posts
- 285
-
11-15-2012, 11:56 PM #8
New Guest
- Join Date
- Nov 2012
- Posts
- 3
I was able to override both circuit EXV's to open 100% and compared the two. The one that im working on only open up 50% when looking through the sight glass while the other one looks like a 100% open. Tried banging it with a wrench to see if it was stuck but that did not work. Gonna change out the EXV motor. You guys are funny!
-
11-16-2012, 12:02 AM #9
New Guest
- Join Date
- Nov 2012
- Posts
- 3
Increased1
I was able to override both circuit EXV's to open 100% and compared the two. The one that im working on only open up 50% when looking through the sight glass while the other one looks like a 100% open. Tried banging it with a wrench to see if it was stuck but that did not work. Gonna change out the EXV motor. You guys are funny!