Results 1 to 8 of 8
    Jan 2001
    Trane voyager troubles
    I have a ych240a3h0ab. The unit is cycling on limit switch. I have 65 return 130 supply. This is in a church diffucult to get cfms. The gas at manifold -.02. I am going to clean evap coil. I did take duct apart and airflow seems ok. I may have to traverse. The heat exchanger looks ok. This unit is 20 years old. The inducer, ignitor and high limit were replaced. Does anyone know what the temp rise should be?? Any thoughts
    Southeastern Pa
    I don't have the spec for temp rise, but it does sound to me as though you are on the right track looking at airflow...
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Nov 2007
    Mississippi
    Sounds like airflow to me too.
    Quote Originally Posted by hvac17011 View Post
    25-55 deg.
    Send me an email (address is in my profile) and I will send you some info on this unit.
    Dec 2003
    Northern VA
    All diffusers open?
    "Iron sharpeneth iron..."
    Jun 2006
    midwest
    I dont know if you meant -.2 I.W.C. , but thats the spec on that unit.
    NH
    I seem to find a lot of fire dampers tripped in church's. I would be looking at airflow as well.
    Dec 2003
    Northern VA
    Quote Originally Posted by Dchappa21 View Post
    I have serviced alot of churches over the years and also have commonly found airflow issues. Certain wings and rooms get closed off so that only the office area(s) which are occupied daily are left open in an attempt at economy. If you have a two stage gas on that unit you might want to disconnect the hi fire if you find this airflow situation.