    Setting head presure for WRV help

    Hey group

    Question what pressure should i set the WRV on a refrigeration system or shall i say what head pressure shoud i be shooting for on system? Any refrigerant. Whats temp/pressure is best for maximum effiency?

    I also ran across a sysytem with WRV on the inlet and valve is installed backwards (arrow the opposite direction)

    Thanks guys

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    You need a PT chart
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    306
    Post Likes
    Thread Starter
    Hey group

    Should i be shooting for 90-100 degree condensing temp? Ya 2sac i'll see if i can locate a PT chart i think I've seen them some where

  4. #4
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    [QUOTE=Iceman_pdx;14586791]Hey group

    Should i be shooting for 90-100 degree condensing temp?

    That would depend on which refrigerant you plan on using.

  5. #5
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    There are some Tecumseh's where 130 degrees is your goal. You're head pressure range is no different than an air cooled unit. If it's an ice machine checking the mfg recomendations would be the best bet.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  6. #6
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Thread relocated to the refer section

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.

  8. #8
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    306
    Post Likes
    Thread Starter
    Thanks icemeister

  9. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by icemeister View Post
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.

    You took the fun out of letting him learn
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  10. #10
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by icemeister View Post
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.
    Ya. What this guy said.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •