Results 1 to 10 of 10
    Portland, Or
    Setting head presure for WRV help
    Hey group
    Question what pressure should i set the WRV on a refrigeration system or shall i say what head pressure shoud i be shooting for on system? Any refrigerant. Whats temp/pressure is best for maximum effiency?
    I also ran across a sysytem with WRV on the inlet and valve is installed backwards (arrow the opposite direction)
    Thanks guys
    Oct 2011
    Chicagoland Area
    You need a PT chart
    Portland, Or
    Hey group
    Should i be shooting for 90-100 degree condensing temp? Ya 2sac i'll see if i can locate a PT chart i think I've seen them some where
    Jan 2010
    [QUOTE=Iceman_pdx;14586791]Hey group
    That would depend on which refrigerant you plan on using.
    Oct 2011
    Chicagoland Area
    There are some Tecumseh's where 130 degrees is your goal. You're head pressure range is no different than an air cooled unit. If it's an ice machine checking the mfg recomendations would be the best bet.
    Mount Airy, MD
    Thread relocated to the refer section
    Jul 2000
    Guayaquil, EC
    The industry's standard nominal rating point for water-cooled condensing units is 105F SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.
    Portland, Or
    Thanks icemeister
    Oct 2011
    Chicagoland Area
    You took the fun out of letting him learn
    Jul 2012
    Western KY
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.
    Ya. What this guy said.