Results 1 to 10 of 10
  1. #1
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    52

    Setting head presure for WRV help

    Hey group

    Question what pressure should i set the WRV on a refrigeration system or shall i say what head pressure shoud i be shooting for on system? Any refrigerant. Whats temp/pressure is best for maximum effiency?

    I also ran across a sysytem with WRV on the inlet and valve is installed backwards (arrow the opposite direction)

    Thanks guys

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    You need a PT chart
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  3. #3
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    52
    Hey group

    Should i be shooting for 90-100 degree condensing temp? Ya 2sac i'll see if i can locate a PT chart i think I've seen them some where

  4. #4
    Join Date
    Jan 2010
    Posts
    4,436
    [QUOTE=Iceman_pdx;14586791]Hey group

    Should i be shooting for 90-100 degree condensing temp?

    That would depend on which refrigerant you plan on using.

  5. #5
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    There are some Tecumseh's where 130 degrees is your goal. You're head pressure range is no different than an air cooled unit. If it's an ice machine checking the mfg recomendations would be the best bet.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  6. #6
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,113
    Thread relocated to the refer section

  7. #7
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,793
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.

  8. #8
    Join Date
    Aug 2012
    Location
    Portland, Or
    Posts
    52
    Thanks icemeister

  9. #9
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    Quote Originally Posted by icemeister View Post
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.

    You took the fun out of letting him learn
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  10. #10
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,063
    Quote Originally Posted by icemeister View Post
    The industry's standard nominal rating point for water-cooled condensing units is 105ºF SCT, so set the WRV to the corresponding pressure for the refrigerant you're working with...so from the PT chart, for R22 it would be 210 psig. The same method applies for whatever the refrigerant is.
    Ya. What this guy said.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •