Page 1 of 2 12 LastLast
Results 1 to 13 of 25
  1. #1
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    Post Likes

    chargeing with 404a

    is it ok to charge walk in freezer to full sight glass . no receiver water cooled condenser

  2. #2
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,379
    Post Likes
    Should have a receiver if you have a tx valve.

  3. #3
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,032
    Post Likes
    Quote Originally Posted by Dchappa21 View Post
    Should have a receiver if you have a tx valve.
    Not if it's not a pumpdown. Might just be using a t-stat to control compressor. A clear glass would be a starting point. SC & SH would be the proper way to go. Make sure the water regulating valve is set properly.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  4. #4
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    Post Likes
    Thread Starter
    cycles on liquid line solinoid valve.compressor took a poop, was called to change out. copeland copelematic m. nrdi 031a tcf 800. going to change oil to ester before install. as well as ll drier and contactor. noticed someone has added suction drier canister with one core.no idea on history,not to familiar with low temp systems. thats why im asking about the charge.thanks

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    4,425
    Post Likes
    No receiver ??

    Is this condenser indoor on top of freezer ?

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    6,032
    Post Likes
    You've got a receiver. Check under the condensing unit
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  7. #7
    Join Date
    Oct 2012
    Posts
    10
    Post Likes
    Yeaa full sight glass is a good start but then after you notice the bubbles just starting to disappear, start doing SH and SC. You don't want to over charge..

  8. #8
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    845
    Post Likes
    Yeah, I bet there is a receiver under the unit.

  9. #9
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,090
    Post Likes
    I bet the condenser is also the receiver.

  10. #10
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    Post Likes
    Thread Starter
    looks like discharge line off compressor goes to vessel under compressor then liquid line exits vessel to drier and sight glass then to evap to freezer. vessel has water line going into it with water regulater. regulator has cap tube that senses pressure via discharge port, then another line exiting vessel dumping water to open sight drain. dont see any receiver.

  11. #11
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    Post Likes
    Thread Starter
    have picture on iphone not sure how to post sorry

  12. #12
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,080
    Post Likes
    Quote Originally Posted by cannedheat View Post
    looks like discharge line off compressor goes to vessel under compressor then liquid line exits vessel to drier and sight glass then to evap to freezer. vessel has water line going into it with water regulater. regulator has cap tube that senses pressure via discharge port, then another line exiting vessel dumping water to open sight drain. dont see any receiver.
    Someone correct me if I am wrong, but I believe based on the description this is a shell and coil type water cooled condenser and that the shell doubles as a receiver in this setup?

  13. #13
    Join Date
    Feb 2006
    Location
    indiana
    Posts
    77
    Post Likes
    Thread Starter
    so the reciever is the vessel and the condenser water is basicly a coil in the vessel condensing hot gas into liquid and storage before entering liquid line and so on..

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.