    Little Data Center

    These are some pictures of a little Data Center that we just did start-up on yesterday and today. It was a tight timeline. 13 weeks total construction time. It was a re-use of an existing building, they gutted it and when went at it fast and hard. Kudos to our pipefitters that worked (7) 10 hr days a week to meet the deadline. Don't be too harsh on the insulators, this is the last week onsite and the punch lists are in progress.

    There are (15) Liebert IRC's feed by (2) Liebert XD Refrigerant Pump Systems/Chilled Water, (4) Liebert DS CRAC units, (1) 6-Module MultiStack Chiller, and a York air handler for the office spaces. Chilled Water piping is 8" black iron welded. Refer lines to IRC's is 2 1/8.

    Name:  PICT0075.jpg
Views: 1252
Size:  67.4 KBName:  PICT0085.jpg
Views: 1155
Size:  23.6 KBName:  PICT0084.jpg
Views: 1176
Size:  34.3 KBName:  PICT0083.jpg
Views: 1196
Size:  54.7 KBName:  PICT0082.jpg
Views: 1158
Size:  18.2 KBName:  PICT0080.jpg
Views: 1130
Size:  29.9 KBName:  PICT0079.jpg
Views: 1137
Size:  41.6 KBName:  PICT0078.jpg
Views: 1099
Size:  39.7 KBName:  PICT0077.jpg
Views: 1100
Size:  51.3 KBName:  PICT0087.jpg
Views: 1077
Size:  30.1 KB

  2. #2
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    wow ...lots of work...looks great.....
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  3. #3
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    If thats little, what would you call large? Looks great.

  4. #4
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    1,092
    Post Likes
    Thread Starter
    Thanks. There is only 900 lbs of refrigerant in the system. Close to being a big system, but not quite. I can't take credit for the pipe work. Our pipefitters really busted ass on this one and did it in a professional manner. Wicked proud of them. Us service guys are only responsible for the equipment.

  5. #5
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    I am an old fart.... i like seeing good. work...very well done..............
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  6. #6
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Awesome job! Were you responsible for the startup of those sweet new Lieberts and the XD system, or did the local Liebert rep do it? Or are you the local Liebert rep?

    Gotta say I am not a big fan of those Airstack chillers, lol
    Don't pick the fly crap out of the pepper.

  7. #7
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    1,092
    Post Likes
    Thread Starter
    We requested and got a guy from the Liebert Factory Service Team to help with the startup of the XD system, since it is new. The local rep wasn't comfortable signing off on it. We are not a Liebert Rep, but I have been to a lot of their training. I started up the CRACs (only hard part is integrating with the BAS).

    I am not a fan of the MultiStax either. This was a spec job. One of those where you don't deviate from the plans at all, just so the chain of finger pointing can continue upward if something doesn't work.

  8. #8
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,886
    Post Likes
    New construction, oh how I sometimes miss it. Great installation. Gotta love a service guy who appreciates a good install crew.
    You need to put the phone down and get back to work!

  9. #9
    Join Date
    Sep 2005
    Posts
    156
    Post Likes
    Beautiful job, I have a data center with about 900 tons of Liebert DX units that are all upflow, they are extremely loud.

  10. #10
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    1,092
    Post Likes
    Thread Starter
    Yes the Liebert DS CRAC units are loud. They will blow your hat off if your infront of them on startup. The new XD/DCP system is pure refrig pump. No compressor in the system, except at the chiller. Gotta say that I was skeptical when I first saw it at the training, but it seems to work. The receiver tank in each of the two DCP modules holds 160 lbs of R-134. We have the XD IRC's setup with a top/bottom configuration. I probably would have combined it with a Lee Temp to take advantage of the low ambient temps here, but I am not an engineer and no one asks me.

    I passed along the kudos to the fitters.

  11. #11
    Join Date
    Dec 2006
    Location
    new england
    Posts
    791
    Post Likes
    Good Stuff. Id like to be in all phases of the project. From install, start-up and future maintance. Nice leibert job. Fitz...
    Chaos equals cash$$$

  12. #12
    Join Date
    Oct 2012
    Posts
    18
    Post Likes
    nice

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •