    Quote Originally Posted by itsiceman View Post
    So you never really did 1)
    Yeah, this made me wonder DIY.

  2. #15
    Join Date
    Dec 2011
    Location
    New Zealand
    Posts
    1,979
    Did you check voltage when it is running? If not, well????

    But I will take a guess, on copeland scrolls, discharge pressure is the biggest single factor on power draw (presume voltage is good), because you have fit more than one, then i will say that you pressure port is being influenced by flow, like a venturi.

    New pressure tapping required.

  3. #16
    Join Date
    Nov 2012
    Posts
    23
    Quote Originally Posted by Sicofthis View Post
    Edit: Removed my reply becoming too DIY. Apply for a pro account.
    not sure what that means....we did some more checking last night...the CPR valve may be an issue but too soon to say....also we probably do have too much R22 in the system and we are removing some...this may be part of the problem...more later...we need to check a few more things...thanks for all the suggestions so far nothing definite

  4. #17
    Join Date
    Nov 2011
    Location
    USA
    Posts
    333
    Quote Originally Posted by barbar View Post
    Did you check voltage when it is running? If not, well????
    And measuring at the disconnect doesn't eliminate a voltage problem.

  5. #18
    Join Date
    Nov 2012
    Posts
    23
    Quote Originally Posted by Saturatedpsi View Post
    And measuring at the disconnect doesn't eliminate a voltage problem.
    technically you are correct, however, the voltage at the disconnect is effectively the voltage at the motor in this case ,..there is 3 ft of copper wire from the disconnect to the starter, 2 feet from the starter to the motor and all wires are good....if we had a bad wire it would have shown up...in this case we do not have a voltage problem..thanks for your input

  6. #19
    Join Date
    Nov 2012
    Posts
    23
    we can actually measure the discharge pressure in several places in the piping...the discharge pressure is a good reading....but you do have a good point...I have seen this problem before but more like a pitot tube...

    we checked some more last night and are wondering if the CPR valve may not be working properly...a simple regulator but perhaps it is stuck.. will check some more thanks

  7. #20
    Join Date
    Nov 2012
    Posts
    23
    the more we look at it it appears the CPR valve is the problem see this link

    http://www.real-world-refrigeration....-valves-3.html

    will let everyone know if this is the problme..thanks

  8. #21
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,002
    First of all, you need to measure voltage at the terminals, because you can't assume you don't have a bad wire, a bad crimp or a bad connection at the compressor itself. Second are you a homeowner or a technician?

  9. #22
    Join Date
    Nov 2011
    Location
    USA
    Posts
    333
    Got my doubts, based on the reported suction pressures, but I'm not there so...

  10. #23
    Join Date
    Nov 2012
    Posts
    23
    I am a licensed professional electrical and nuclear engineer with extensive expereince.

  11. #24
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,002
    In that case this thread belongs in the AOP section.

    I am the son of an engineer and I have really extensive experience and I can tell you that there is a broad difference between being an engineer and being the guy who fixes things. This is mainly manifested in the difference between the world of theory and the world of reality.

    Btw, Butch was my name my parents called me until I went to private school!

  12. #25
    Join Date
    Nov 2011
    Location
    USA
    Posts
    333
    Quote Originally Posted by Butch1234 View Post
    I am a licensed professional electrical and nuclear engineer with extensive expereince.

    You're over-qualified for heat pump diagnostics...

  13. #26
    Join Date
    Nov 2011
    Location
    USA
    Posts
    333
    Quote Originally Posted by timebuilder View Post
    In that case this thread belongs in the AOP section.
    Please make an exception in this case...I'd really like to see the final analysis/diagnosis.

Page 2 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event