Results 1 to 13 of 13
Thread: Trane RTAC POE oil
-
11-12-2012, 06:51 PM #1
Professional Member
- Join Date
- Mar 2004
- Location
- Texas
- Posts
- 34
Trane RTAC POE oil
We have three 400 ton RTAC chillers that are 3 years old with 134a.
Last year they had the butterfly valve leaks and one went flat.
A contractor changed them out on all three chillers.
All went well.
Had the yearly service done and that included an oil analysis.
Last year all chillers before the valve issues had about 125 PPM of water.
Now they got 500 to 600 PPM.
Can anyone tell me is that is going to be a problem?
What level of water is cause for concern?
How to dry out? Just replace the drier cores?
I am getting conflicting opinions from people on this and need clarification.
Thanks
-
11-12-2012, 07:06 PM #2
I've seen some issues with moisture contamination while the sample was in transit. If you're going to pull oil samples on these machines, you need to use a glass bottle with a gasketed cap. There are no drier cores to be replaced on any RTAC manufactured before 2011, either. Because of POE's affinity for moisture, the oil is the drier in the system. I have a document somewhere with the numbers. I'll try and find it for you. Paradoxically, R-134A systems are more forgiving than R-22 systems where moisture is concerned.
If the circuit went flat and was allowed to sit open for more than a day or so, I would have recommended an oil change on this circuit.Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
11-12-2012, 07:15 PM #3
if there is ever a concern with an oil sample, then you need to resample. another oil sample and report is much cheaper than any chiller repair.
Spellin mitsakes bother me.
-
11-12-2012, 08:13 PM #4
rob
we use national for our samples, who is supplying you with a glass bottle
-
11-12-2012, 08:16 PM #5
300 ppm I believe is max trane wants to see on oil48. change oil. is moisture indicator at exv yellow? if so, maybe a bypass filter, have a hose leaving the liquid line angle valve with a flare dryer, 303, entering into 3/8 line at the bottom of the evap and just crack the valve open at the evap.
-
11-12-2012, 10:31 PM #6
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,505
-
11-12-2012, 10:45 PM #7
think its a strainer
-
11-12-2012, 11:42 PM #8Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
11-13-2012, 08:30 AM #9
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 860
There is only a paper element in the single core shell. There never was a drier in there (even before 2011). Don't put a drier in there. If cleanup is needed, make a cleanup kit by putting a drier and sight glass between the liquid line and bottom of evap like R404a described.
-
11-13-2012, 09:02 AM #10
And I believe that this scavenger line has to have a slope ., I recall a SB on this.
-
11-13-2012, 07:37 PM #11
Professional Member
- Join Date
- Mar 2004
- Location
- Texas
- Posts
- 34
Thanks for all your help.
Never knew there was not a drier in there, these machines are new to me.
Most of my chiller experience up to now has been with RTAA machines.
I will take the cheap route and send the oil off to another lab for retesting and see what happens.
BTW the lab that we got the results from states 200ppm of water is the upper limit.
Got a call into Trane to see what they think but the local office is not real good at responding real fast.
-
11-13-2012, 08:35 PM #12
Professional Member
- Join Date
- Jan 2011
- Location
- Central, PA
- Posts
- 90
Funny you mention a glass bottle. We get and send our oil samples out to Trane and they give you plastic bottles in the kits. above 300ppm is cause for concern.
-
11-13-2012, 11:16 PM #13Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!


Reply With Quote