    Trane RTAC POE oil

    We have three 400 ton RTAC chillers that are 3 years old with 134a.

    Last year they had the butterfly valve leaks and one went flat.
    A contractor changed them out on all three chillers.
    All went well.

    Had the yearly service done and that included an oil analysis.

    Last year all chillers before the valve issues had about 125 PPM of water.
    Now they got 500 to 600 PPM.

    Can anyone tell me is that is going to be a problem?
    What level of water is cause for concern?

    How to dry out? Just replace the drier cores?

    I am getting conflicting opinions from people on this and need clarification.

    Thanks

  2. #2
    Join Date
    Mar 2007
    Posts
    3,108
    I've seen some issues with moisture contamination while the sample was in transit. If you're going to pull oil samples on these machines, you need to use a glass bottle with a gasketed cap. There are no drier cores to be replaced on any RTAC manufactured before 2011, either. Because of POE's affinity for moisture, the oil is the drier in the system. I have a document somewhere with the numbers. I'll try and find it for you. Paradoxically, R-134A systems are more forgiving than R-22 systems where moisture is concerned.

    If the circuit went flat and was allowed to sit open for more than a day or so, I would have recommended an oil change on this circuit.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,388
    if there is ever a concern with an oil sample, then you need to resample. another oil sample and report is much cheaper than any chiller repair.
    When I am late for work, I usually make up for it by leaving early.

  4. #4
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,141
    rob

    we use national for our samples, who is supplying you with a glass bottle

  5. #5
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,141
    300 ppm I believe is max trane wants to see on oil48. change oil. is moisture indicator at exv yellow? if so, maybe a bypass filter, have a hose leaving the liquid line angle valve with a flare dryer, 303, entering into 3/8 line at the bottom of the evap and just crack the valve open at the evap.

  6. #6
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,720
    So is the single core shell empty ?

    Quote Originally Posted by Tech Rob View Post
    I've seen some issues with moisture contamination while the sample was in transit. If you're going to pull oil samples on these machines, you need to use a glass bottle with a gasketed cap. There are no drier cores to be replaced on any RTAC manufactured before 2011, either. Because of POE's affinity for moisture, the oil is the drier in the system. I have a document somewhere with the numbers. I'll try and find it for you. Paradoxically, R-134A systems are more forgiving than R-22 systems where moisture is concerned.

    If the circuit went flat and was allowed to sit open for more than a day or so, I would have recommended an oil change on this circuit.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  7. #7
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,141
    think its a strainer

  8. #8
    Join Date
    Mar 2007
    Posts
    3,108
    Quote Originally Posted by Dallas Duster View Post
    So is the single core shell empty ?
    It's not empty, but it has a paper filter cartridge in it. It's just there to catch debris. There is a very small strainer in the scavenger line going from the evaporator to the compressor.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  9. #9
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,317
    There is only a paper element in the single core shell. There never was a drier in there (even before 2011). Don't put a drier in there. If cleanup is needed, make a cleanup kit by putting a drier and sight glass between the liquid line and bottom of evap like R404a described.

  10. #10
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    And I believe that this scavenger line has to have a slope ., I recall a SB on this.

  11. #11
    Join Date
    Mar 2004
    Location
    Texas
    Posts
    35
    Thanks for all your help.

    Never knew there was not a drier in there, these machines are new to me.

    Most of my chiller experience up to now has been with RTAA machines.

    I will take the cheap route and send the oil off to another lab for retesting and see what happens.

    BTW the lab that we got the results from states 200ppm of water is the upper limit.

    Got a call into Trane to see what they think but the local office is not real good at responding real fast.

  12. #12
    Join Date
    Jan 2011
    Location
    Central, PA
    Posts
    105
    Funny you mention a glass bottle. We get and send our oil samples out to Trane and they give you plastic bottles in the kits. above 300ppm is cause for concern.

  13. #13
    Join Date
    Mar 2007
    Posts
    3,108
    Quote Originally Posted by R123 View Post
    There is only a paper element in the single core shell. There never was a drier in there (even before 2011). Don't put a drier in there. If cleanup is needed, make a cleanup kit by putting a drier and sight glass between the liquid line and bottom of evap like R404a described.
    The drier I was referring to was the one added to replace the 3/8" wye strainer in the scavenger line.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event