    new Lennox SL280v not set up for two stage

    I have a quick question regarding our new upstairs furnace that was installed last July.

    Our Lennox SL280v was never wired for "true" 2-stage operation, so the unit runs on low fire for 7 minutes then switches to high. My question is, is it better to have true 2-stage operation where the furnace will only run in high stage when it needs to or is the setup fine the way it currently is? I would like to have true 2-stage operation but I want your opinions on it first. I'm surprised how the installers never ran a W2 wire to the thermostat. The technician who performed our furnace tune-up/inspection several weeks ago said that he could add a wire but said it was optional and it is not impossible to have one added. The thermostat is a Honeywell RTH6450D and it is compatible with multi-stage systems.

  2. #2
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,437
    Post Likes
    Up to you. Set up as a two stage via the thermostat gives longer run times and increased comfort. Second stage has a better combustion efficiency so getting there from the timer is not a bad thing.

  3. #3
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,282
    Post Likes
    As Marty stated. Having w1 and w2 hooked up at stat will be more comfortable to others.

    Having the furnace fire in only w2 will save you more energy and give you the most heat.

    A lot of people are against me but, I only set furnaces to high fire and tune them with a combustion analyzer. With certain formulas and data I can prove high fire costs less money and gives you more heat.

  4. #4
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Thanks for the input. I appreciate it. Our upstairs is 1400 sq. ft. and the furnace is 66,000 BTU input on second stage and 43,000 BTU input on first stage. Our furnace is the smallest size the SL280v it comes in. I think that having true two stage control will probably be more ideal because with the furnace running on low the majority of the time, it won't short cycle and will provide more comfort. Also since the upstairs only being 1400 sq. ft., 66,000 BTU sounds a bit too much so that will make the furnace rarely run on second stage.

  5. #5
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,045
    Post Likes
    I feel it's just laziness on the part of the install company to sell a 2 stage furnace then not wire it properly, I wll say where I work they do the same crap
    Go Trump

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,642
    Post Likes
    Have it set up for 2 satage operation by the thermostat. It provides better comfort, by not giving you that sudden cool feeling when it shuts off like single stage furnaces do, or just running in high fire.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Dec 2007
    Posts
    7,222
    Post Likes
    Quote Originally Posted by catmanacman View Post
    I feel it's just laziness on the part of the install company to sell a 2 stage furnace then not wire it properly, I wll say where I work they do the same crap
    X2

    and the funny thing is the guys where I work say they set it up right, but the manual is still sealed in the package and I know they do not have the info from another source.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    I'd just disable the 2nd stage entirely, it's not like you need it. The only time I would see the 2nd stage being handy is if you setback your thermostat at night and want it to warm up quickly in the morning.

  9. #9
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    That's a modulating furnace, it shouldn't be set up for 2 stage operation anyways.

  10. #10
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Thanks everyone for the recommendations. I can tell that obviously having the 2 stage control can provide better comfort.

    Quote Originally Posted by 54regcab View Post
    I'd just disable the 2nd stage entirely, it's not like you need it. The only time I would see the 2nd stage being handy is if you setback your thermostat at night and want it to warm up quickly in the morning.
    We always set back our thermostat at night time like for instance the thermostat is set at 67* all night and in the morning the setting goes up to 71*. That will probably be the only time the furnace will ever run in 2nd stage.

  11. #11
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,374
    Post Likes
    Quote Originally Posted by syndicated View Post
    That's a modulating furnace, it shouldn't be set up for 2 stage operation anyways.
    No it isn't. The SLP98v is modulating. The SL280V is a 2-stage, variable speed 80% furnace.

  12. #12
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    I knew that syndicated was wrong because I clearly checked Lennox's website.

  13. #13
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,282
    Post Likes
    If your going to run in 1st stage all the time, have someone verify operation with combustion analyzer to make sure your flue gases are hot enough and they wont condense before leaving exhaust pipe, which would eat away the flue pipe and heat exchanger.