Results 1 to 9 of 9
  1. #1
    Join Date
    Sep 2008
    Location
    SouthEastern Wisconsin
    Posts
    166
    Post Likes

    Make space temperature Calibration with Niagara AX

    O.K. I have Niagara AX. With a Lon Based stat pulled into my JACE. The actual apacetemp is about 3 degrees lower than what the space sensor is reading. I know there is a way to enter an adjustment into the spacetemp point, I just don't remember how. Can anyone help me?
    Normal is just a setting on the washing machine...

  2. #2
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    1,791
    Post Likes
    On a Lon based stat I would think the calibration needs to be done at the stat, if not the stat will still see the wrong value and control by it. To change a reading AX side in the point properties under facets, conversion, linear and add offset value.

  3. #3
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    Quote Originally Posted by hvac69 View Post
    On a Lon based stat I would think the calibration needs to be done at the stat, if not the stat will still see the wrong value and control by it. To change a reading AX side in the point properties under facets, conversion, linear and add offset value.
    ...ProxyExt/Conversion/Linear ... and add offset value.
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  4. #4
    Join Date
    Oct 2007
    Location
    England
    Posts
    348
    Post Likes
    Usually there is a SNVT 'SensOffset' or something like that in the Lon wall sensor itself.

    I know that it can be done through the plugin for Honeywell XL-10's and a few Thermokon sensors I have come across.

  5. #5
    Join Date
    Nov 2012
    Posts
    10
    Post Likes
    If this device is the unit controller and not just a network temperature you will want to find the calibration snvt like Keith mentioned. Otherwise by adjusting the proxy extention, you will only be calibrating what the user sees, but not the actual temperature control.

  6. #6
    Join Date
    Sep 2008
    Location
    SouthEastern Wisconsin
    Posts
    166
    Post Likes
    Thread Starter
    I attempted to adjust the space temp by going ...ProxyExt/Conversion/Linear ... and add offset value. My space temp reading went from 78.4 to 26. I have a Bapi lon stat pulled into a Circon controller (which is controlling a rooftop unit) and this is pulled into our Jace. I do not know where to find my lon snvt's for this stat. Any suggestions?
    Normal is just a setting on the washing machine...

  7. #7
    Join Date
    Nov 2012
    Posts
    10
    Post Likes
    There should be a "nciTmpOffset"

  8. #8
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    539
    Post Likes
    [QUOTE=nuclear rabbit;14583531]I attempted to adjust the space temp by going ...ProxyExt/Conversion/Linear ... and add offset value. My space temp reading went from 78.4 to 26. I have a Bapi lon stat pulled into a Circon controller (which is controlling a rooftop unit) and this is pulled into our Jace. I do not know where to find my lon snvt's for this stat. Any suggestions?[/QUOTE

    I think it was converted to Celsius, you need the offset point to be a snvt type 147.

  9. #9
    Join Date
    Oct 2007
    Location
    Huntsville, AL
    Posts
    419
    Post Likes
    Quote Originally Posted by nuclear rabbit View Post
    I attempted to adjust the space temp by going ...ProxyExt/Conversion/Linear ... and add offset value. My space temp reading went from 78.4 to 26. I have a Bapi lon stat pulled into a Circon controller (which is controlling a rooftop unit) and this is pulled into our Jace. I do not know where to find my lon snvt's for this stat. Any suggestions?
    Do you have the Circon wizards?? You should be able to do it through the wizards.


    Im like a mushroom, they keep me in the dark and feed me crap.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.