Originally Posted by
must
follow manufacturers instructions.
I've never seen a manufacturer instructions that dictate supply placement.
603.7 Rigid duct penetrations. Duct system penetrations of walls, floors, ceilings and roofs and air transfer openings in such building components shall be protected as required by Section 607. Ducts in a private garage and ducts penetrating the walls or ceilings separating a dwelling from a private garage shall be continuous and constructed of a minimum 26 gage [0.0187 inch (0.4712 mm)] galvanized sheet metal and shall not have openings into the garage. Fire and smoke dampers are not required in such ducts passing through the wall or ceiling separating a dwelling from a private garage except where required by Chapter 7 of the International Building Code.
International Mechanical Code, 2009.
No openings. Even a supply.
UNLESS:
The system that heats the garage, heats no other space. Then, essentially, all rules dictating supply/return placement in a garage don't apply.
"Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."