    Honeywell M9185D 1994 Modutrol Troubleshooting:

    The Modutrol Motor is a M9165D1004.

    I have a customer with a large heat recovery unit in a nursing home. There are a few Modutrol motors in the unit but there is one that operates a hot water heating valve. It is operated by a Honeywell T991A potentiometer control. The valve stopped working. I can make it open by jumping from the 24 volt Red to the Blue. It has a spring close. If I remove power, it closes. The T991A is supposed to modulate the valve open to control the air temperature inside the air exchanger. I got the manual for the Modutrol online but it doesn't tell me how to test it to see what might be wrong with it.

    Any electrician that I ask gets that glazed look in their eye. I understand how it works, just not how to tell what it is doing wrong. I can't figure out how to test it electrically. Or if it can be fixed. The motor works, it just won't modulate and control the temperature in the building.

    How do you test it and what do you look for?

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    663
    Post Likes
    Basic Series 90 set up and trouble shooting is covered in this document http://96.61.63.50/techlib/Honeywell...190_632195.pdf
    UA LU 562

  3. #3
    Join Date
    Oct 2008
    Location
    Royal Palm Beach, FL
    Posts
    395
    Post Likes
    Thread Starter
    Thanks Dave,

    That's what I need. Someone at heatinghelp.com sent me a couple of PDF's on them and I got the idea. If you connect red toi blue and white, and the valve goes half way, replace the motor.

    It's too bad that there isn't something like what you posted in the box. But it usually doesn't matter because some half wit meintenance person will throw the whole mess out in the trash. And then get pissy when you can't solve the problem in ten minutes. After they spent hours on it. Or, they didn't know that there was a problem, other than they were getting complaints that the building was cold.

    Thanks for the help.